I have just installed 2 x Halogen 500W floodlights together with a PIR. These are installed on it's own circuit connected to a B6 MCB. There is nothing else on the circuit. All wiring is 1.5mm.
I am having intermittant trip on the MCB when the lights are activated. The trip is not happening all the time! If I reset the trip the lights will work fine, it seems to trip after a long period of inactivity (Not everytime).
Should I be looking for a fault or is this a problem with a marginal surge current.
If the latter I believe I have a number of options, downgrade to 300W (don't really want to do this), change to a C6 MCB or change to B10 MCB (seems to be an overkill for a 1kW circuit)
Any suggestions or comments.
Dave
I am having intermittant trip on the MCB when the lights are activated. The trip is not happening all the time! If I reset the trip the lights will work fine, it seems to trip after a long period of inactivity (Not everytime).
Should I be looking for a fault or is this a problem with a marginal surge current.
If the latter I believe I have a number of options, downgrade to 300W (don't really want to do this), change to a C6 MCB or change to B10 MCB (seems to be an overkill for a 1kW circuit)
Any suggestions or comments.
Dave