2391 practical

Discussion in 'Electrics UK' started by andy1984, 12 Aug 2006.

  1. andy1984

    andy1984

    Joined:
    3 Aug 2006
    Messages:
    34
    Thanks Received:
    0
    Country:
    United Kingdom
    hi

    on the 2391 practical when doind the first test, continuity of circuit protective conductors can i take out the phase conductor for the circuit under test and put it into the earth bar thus getting the R1+R2 aswell to save time?

    main question though is do i have to disconnect any other earths from the main earth terminal before doing this?

    such as the main earth or supp bonding? bit confused on the parralel paths subject.

    at what point do i disconnect earths and for what earths and for what reason?

    cheers guys.
     
  2. cozycats

    cozycats

    Joined:
    8 Nov 2005
    Messages:
    186
    Thanks Received:
    4
    Country:
    United Kingdom
    READ GN3 and do all tests as described!!!!
     
  3. Sponsored Links
  4. The Jeep

    The Jeep

    Joined:
    22 Jun 2006
    Messages:
    249
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Parallel paths only exist where they make a complete circuit at the point of measurement. If you test, say, between the disconnected earth of a lighting circuit and the earth bar in the CU where the lighting circuit earth is connected, even with your main earth bonding and other circuits' earths connected to the bar, you are only measuring the resistance of the lighting circuit earth between the CU and the other disconnected end.

    If you hadn't disconnected at least one of the ends, then you would be getting into parallel path territory. Just remember that the test current has to flow in a complete loop. Any incomplete loops will have no effect on the measurement.
     
  5. comms

    comms

    Joined:
    13 Nov 2004
    Messages:
    882
    Thanks Received:
    8
    Location:
    Berkshire
    Country:
    United Kingdom
    Or put a link in between the met and the phase conductor (mcb) of the circuit your wanting to get the R1+R2 / continuity of cpc from, and test at furthest point of circuit, then just move the link on to the phase conductor of the next circuit your wanting to test cpc continuity of, leaving the other end of link connected to the met.
    Don't forget to remove the link when you've completed cont testing.
    But has already said take a look at GN3 or osg.
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page