    Big conventional boiler, no ABV in the system afaik. Are they readily available for 42mm pipes?
     
  2. Sponsored Links
  3. jeff the gasman

    jeff the gasman

    Joined:
    8 Dec 2007
    Messages:
    13,777
    Thanks Received:
    5,096
    Location:
    Cheshire
    Country:
    United Kingdom
    Firstly, what’s an ABV?
     
    • Like Like x 1
  4. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    Automatic bypass valve
     
  5. jeff the gasman

    jeff the gasman

    Joined:
    8 Dec 2007
    Messages:
    13,777
    Thanks Received:
    5,096
    Location:
    Cheshire
    Country:
    United Kingdom
    42 x 42 x 22 tee. with 22mm bypass.
     
  6. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,945
    Thanks Received:
    1,294
    Location:
    Potters Bar
    Country:
    United Kingdom
    Alcohol by Volume ;)
     
    • Like Like x 4
  7. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    I'd have thought if the boiler has such big feed and return pipes, the bypass would have been a beefier thing than the usual 22mm, but hey, what do I know.
     
  8. jeff the gasman

    jeff the gasman

    Joined:
    8 Dec 2007
    Messages:
    13,777
    Thanks Received:
    5,096
    Location:
    Cheshire
    Country:
    United Kingdom
    Not much?
     
    • Like Like x 2
  9. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,779
    Thanks Received:
    1,096
    Country:
    United Kingdom
    A shunt pump.
     
    • Like Like x 1
  10. Sponsored Links
  11. fixitflav

    fixitflav

    Joined:
    20 Mar 2018
    Messages:
    1,235
    Thanks Received:
    139
    Location:
    Stoke-on-Trent
    Country:
    United Kingdom
    If it's an existing system and there isn't one currently, what makes you think you need one? Just curious
     
    • Like Like x 1
  12. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    13,342
    Thanks Received:
    3,077
    Location:
    Daventry
    Country:
    United Kingdom
    The bypass only has to be able to carry the minimum volume of water required by the boiler, not the full system flow. They're specified by looking in the boiler manufacturer's instructions, finding out what the minimum flow requirement is, then finding an ABV that will deliver that flow. 28mm ones are available if 22mm really won't do it. Larger systems will almost always have a header and so an ABV is not required
     
  13. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    That coming from someone who asked what an ABV was?
     
    • Like Like x 1
  14. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    System was fitted in the early 90s before ABVs were wide spread. There have been instances when the TRVs have closed off enough to force the hot water out the overflow on the roof. Crossed my mind having an ABV added might help.
     
  15. fixitflav

    fixitflav

    Joined:
    20 Mar 2018
    Messages:
    1,235
    Thanks Received:
    139
    Location:
    Stoke-on-Trent
    Country:
    United Kingdom
    Interesting. Usually there is at least one rad without a TRV (the one where the roomstat is), so the boiler gets minimum flow if all the TRVs close. But if all have TRVs and all close, I can't see why the F/E tank would overflow, if that's what you're saying. Though the boiler wouldn't like it. As a stopgap, you could remove the head from one TRV.
     
  16. jeff the gasman

    jeff the gasman

    Joined:
    8 Dec 2007
    Messages:
    13,777
    Thanks Received:
    5,096
    Location:
    Cheshire
    Country:
    United Kingdom
    You need to sort out the hydraulics rather than finding a way around it.
     
  17. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,575
    Thanks Received:
    9,765
    Location:
    Lanarkshire
    Country:
    United Kingdom
    An ABV wont stop pumping over, you have bigger system design problems than that
     