Acrow prop specs

Joined
17 May 2008
Messages
8,416
Reaction score
1,129
Country
United Kingdom
Why the kilo newton techno jargon?
Its 10 ton.
I'd put 12 props under that assuming they are not extended.
 
Sponsored Links
Joined
7 Nov 2008
Messages
145
Reaction score
1
Location
Mid Glamorgan
Country
United Kingdom
Are we going to be told what this mystery load is, and why spacing of props is irrelevant?

The spacing cannot be deduced until the number of props are established. This is simple common sense.
Read previous threads for job in question Im not repeating it here.
 
Joined
7 Nov 2008
Messages
145
Reaction score
1
Location
Mid Glamorgan
Country
United Kingdom
Im trying to find specs for standard UK acrow props. Im needing to calc how many I need for the job. Will use a No1 or 2 prop extended to 2.5m
Can anyone help

For both number 1` and 2 acrows, we work to the following safe working loads.
10% open 35kN
50% open 30kN
Fully open 25kN
As we do not know whether you are needling or sole and plate shoring, can give you no further advice.
Regards oldun

Thanks oldun, most useful
Those values are much higher than the values in the australian table i my first post. Do you know if Acrows differ significantly around the world.
 
Sponsored Links
Joined
7 Nov 2008
Messages
145
Reaction score
1
Location
Mid Glamorgan
Country
United Kingdom
Why the kilo newton techno jargon?
Its 10 ton.
I'd put 12 props under that assuming they are not extended.

The quoted load is in kN as its taken from my calculations to deduce UB size and they are worked out using kN.
Calculations are done in Newtons as this is a unit of force, and we are dealing with force. Tonne is mass which is constant. Force can change depending on a number of factors.
Take the Acrow, if it is dead vertical and is supporting mass of 1 tonne then this is a force of 10kN. But if the acrow is tilted the mass remains the same but the force splits into two components, a vertical and horizontal both less than the original but adding up to the original. The vertical now becomes less, this is why force is used in these calculations instead of mass
 
Joined
3 Sep 2006
Messages
36,464
Reaction score
5,141
Location
West Mids
Country
United Kingdom
**** me, it's like some top secret MI6 job, or the OP is on an old modem and being charged per byte of information uploaded .... and is too tight to go near his allowance.
 
Joined
7 Nov 2008
Messages
145
Reaction score
1
Location
Mid Glamorgan
Country
United Kingdom
f***** me, it's like some top secret MI6 job, or the OP is on an old modem and being charged per byte of information uploaded .... and is too tight to go near his allowance.

Woody read the posts your question has been answered about twice I think
 
Joined
23 Feb 2012
Messages
10,557
Reaction score
1,719
Location
Manchester
Country
United Kingdom

The quoted load is in kN as its taken from my calculations to deduce UB size [/quote]

Factored or unfactored? - it makes a difference.
 
Joined
17 May 2008
Messages
8,416
Reaction score
1,129
Country
United Kingdom
Why the kilo newton techno jargon?
Its 10 ton.
I'd put 12 props under that assuming they are not extended.

The quoted load is in kN as its taken from my calculations to deduce UB size and they are worked out using kN.
Calculations are done in Newtons as this is a unit of force, and we are dealing with force. Tonne is mass which is constant. Force can change depending on a number of factors.
Take the Acrow, if it is dead vertical and is supporting mass of 1 tonne then this is a force of 10kN. But if the acrow is tilted the mass remains the same but the force splits into two components, a vertical and horizontal both less than the original but adding up to the original. The vertical now becomes less, this is why force is used in these calculations instead of mass

Are you an engineer stuck in an office job?
You are wrong about the part highlighted in bold if the load is vertical down.

Oh and btw. You never ever tilt an acrow prop unless absolutely necessary. Back to the drawing board for you son. Or I'll take you out unto site some day propping a few hundred ton of wet concrete. You'll learn more at that then reading a few books.
Especially when it bursts and you're knee deep in the stuff. :LOL:
 
Joined
4 Apr 2008
Messages
1,972
Reaction score
300
Location
Hertfordshire
Country
United Kingdom
Iandandav, people here are trying to help you, but you are making it very difficult for them...

You said "The spacing can't be deduced until the number of props has been determined."
However, this doesn't take into account that, for example, you may only need one prop for the applied load. However, you know very well you would need more than one prop.
So you can determine a minimum number of props for the load, but it won't necessarily be enough. One prop on a five metre span will not hold up the back of your house, regardless of the load applied. You also aren't going to want to space them at more than about 900mm or so, otherwise the brickwork will not arch between them. This is why spacing is also important.

If you use Strongboys and prop from one side only the capacity is greatly reduced due to the cantilever effect of the load applying a moment to the prop.

Finally, you are almost correct when you talk about props at an angle. There will be a horizontal and vertical component, but they are not additive. Forces are vector quantities, so, you use trigonometry or pythagoras to calculate the resultant force.

For example hyp = sqrt (opp² + adj²).

As Norcon said, you shouldn't install acrows at an angle anyway, but there will be an allowance in capacity tables for applied moments from props being slightly off vertical.

Anyway, theoldun has given you the capacity for a single prop. If you don't believe him, call your local tool hire company and they will have the figures available.
 
Joined
3 Sep 2006
Messages
36,464
Reaction score
5,141
Location
West Mids
Country
United Kingdom
What a bloody palaver. :rolleyes: :rolleyes: :rolleyes: :rolleyes: :rolleyes: :rolleyes: :rolleyes:

Out of sheer curiosity, I've gone searching for the mystery structure, and the top secret job.

Contrary to it being an extension to the SIS Building, it seems to be a wall removal in a poxy 3 bed terrace, with a 2.5 m beam holding up a first floor

Four props then. Thread closed
 
Joined
21 Jan 2007
Messages
20,725
Reaction score
2,545
Location
Devon
Country
United Kingdom
Jeez, you bunch of miserable lazy gits, you just cannot be bothered to trawl through the OP's previous threads! Honestly! :rolleyes:
 
Joined
7 Nov 2008
Messages
145
Reaction score
1
Location
Mid Glamorgan
Country
United Kingdom
I used 6, 12 would have been over kill, 2 insufficient.
2.5m was the final span of the opening, the acrows needed to support the whole width of the lounge and hall until the pillars were built. Thanks for all the posts its been amusing.
 