Hi, so our house has a heat loss of about 6kw, (1950's semi, about 100 sqm) but the old oil boiler is a grant 15-26 kw external oil boiler. it's not been in use since we moved in, and is currently disconnected as we removed the old vented hot water system and want to replace with unvented in a different location.
As far as i can find out this oil boiler can't modulate its output meaning that at a minimum it's 9kw in excess of the required heating load (and that heat load is at a dT of 21 afaik, which is only the coldest parts of the year).
The boiler may also be factory set to closer to 20kw output but i don't know.
What could i do to try to make this work better? i would expect it will short cycle, so would adding a pretty large buffer tank help?
In theory it would take between 20 to 30 mins to heat a 100l buffer tank from cold (dT 40C), depending on whether it is actually delivering 15 or 20kw.
this is all new to me, i only found out what buffer tanks did about 5 mins ago so i have a lot to learn about heating systems so value any input.
P.S. eventually i might switch to a heat pump so would like to design a compatible system for that in the longer term.
As far as i can find out this oil boiler can't modulate its output meaning that at a minimum it's 9kw in excess of the required heating load (and that heat load is at a dT of 21 afaik, which is only the coldest parts of the year).
The boiler may also be factory set to closer to 20kw output but i don't know.
What could i do to try to make this work better? i would expect it will short cycle, so would adding a pretty large buffer tank help?
In theory it would take between 20 to 30 mins to heat a 100l buffer tank from cold (dT 40C), depending on whether it is actually delivering 15 or 20kw.
this is all new to me, i only found out what buffer tanks did about 5 mins ago so i have a lot to learn about heating systems so value any input.
P.S. eventually i might switch to a heat pump so would like to design a compatible system for that in the longer term.