Another installation testing issue

Discussion in 'Electrics UK' started by Licklieder, 10 Jul 2021.

  1. Licklieder

    Licklieder

    Joined:
    2 Oct 2010
    Messages:
    114
    Thanks Received:
    4
    Location:
    Surrey
    Country:
    United Kingdom
    So, having completed the replacement of the mcb in my consumer unit with RCBO's I cracked on with testing and hit an issue with the lighting circuit.

    Everything tests out fine - with the exception of the Line-Neutral IR test, which tests out as 0MOhm at 250V. Doing a continuity measurement reveals a Line - Neutral resistance of 175 Ohm.

    I've managed to isolate the issue to the bathroom, but am at a loss to explain what's causing it. I've disconnect the switches, isolated and then disconnected the Fan but i can't get rid of this 175 Ohms. The only hypothesis i can come up with that makes sense is that the dimmable transformers must be permenantly wired in to Line & Neutral, with a seperate line from the dimmer switch to control the lights. Does that make sense ?

    I'd like to get the lights out from the bathroom to see what's up there but am struggling to get the out.
     
  2. Sponsored Links
  3. Swwils

    Swwils

    Joined:
    2 Jul 2020
    Messages:
    757
    Thanks Received:
    137
    Country:
    United Kingdom
    How was the CPC continuity and polarity to each accessory point ?
     
  4. Licklieder

    Licklieder

    Joined:
    2 Oct 2010
    Messages:
    114
    Thanks Received:
    4
    Location:
    Surrey
    Country:
    United Kingdom
    Seemed to test out reasonably ok. When i linked out at the CU & tested at a wall sconce at the end of the run (dimmer linked out) I got continuitiy readings of:

    Line - Earth: 1.71 Ohm
    Line - Neutral : 1.46 Ohm
    Neutral - Earth : 1.59 Ohm​

    Bit more variance than i'd like, but the trip times for the PFC / PSC (>30A) are within spec for the 6A rating. I did find a Neutral / Line had been swapped at one point in the circuit and fixed that - .
     
  5. BS3036

    BS3036

    Joined:
    24 Sep 2007
    Messages:
    944
    Thanks Received:
    68
    Country:
    United Kingdom
    Shaver socket?
     
  6. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,698
    Thanks Received:
    280
    Country:
    United Kingdom
    I personally wouldn't even try to get a L-N insulation resistance test on an existing lighting cirucit with loads like fans and transformers connected. Stick L and N together and test to earth, L-N can go down as lim as its not resonably practicable to do so
     
    • Like Like x 1
  7. Swwils

    Swwils

    Joined:
    2 Jul 2020
    Messages:
    757
    Thanks Received:
    137
    Country:
    United Kingdom
    Possible neon on a hidden fcu?
     
  8. Licklieder

    Licklieder

    Joined:
    2 Oct 2010
    Messages:
    114
    Thanks Received:
    4
    Location:
    Surrey
    Country:
    United Kingdom
    There used to be one that was removed (I hope) when the bathroom was done & the walls tiled. I always assumed that was on the Final Ring Main anyway. Did make me think about the wall cabinet above the sink though - wonder if that's got an isolation transformer in it & if its wired into the lighting circuit. something else to investigate - it need to take it down anyway as a 'guest' snapped off the pull cord for the cabinet light
     
  9. Licklieder

    Licklieder

    Joined:
    2 Oct 2010
    Messages:
    114
    Thanks Received:
    4
    Location:
    Surrey
    Country:
    United Kingdom
    Completely forgot about tieing L-N together to do the IR test - got so focussed on trying to work out what the cause of the reading was it slipped my mind. I'll give that a go when i next power down
     
  10. Sponsored Links
  11. Licklieder

    Licklieder

    Joined:
    2 Oct 2010
    Messages:
    114
    Thanks Received:
    4
    Location:
    Surrey
    Country:
    United Kingdom
    I hope not - the only place for it be hidden would be above the lowered ceiling, and so inaccessible.
     
  12. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,454
    Thanks Received:
    4,199
    Location:
    Retired to:
    Country:
    Portugal
    175Ω L - N is around 330W so will be quite warm if one item.
     
  13. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,886
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    It's about 1.3A so more significant than a neon.

    If its real, worth finding it cus it could reduce your leccy bill!
     
    • Like Like x 2
  14. BS3036

    BS3036

    Joined:
    24 Sep 2007
    Messages:
    944
    Thanks Received:
    68
    Country:
    United Kingdom
    A neon will have a series resistor of at least 10k, more likely much higher.
     
  15. AdrianUK

    AdrianUK

    Joined:
    22 Sep 2009
    Messages:
    611
    Thanks Received:
    91
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Unless it is something transformer based. If the OP is measuring the DC resistance of a small transformer, its AC impedance will be much higher & hence pulling nothing like 330W at 50Hz
     
    • Like Like x 2
  16. zebedee2001

    zebedee2001

    Joined:
    5 Mar 2008
    Messages:
    84
    Thanks Received:
    4
    Location:
    Norfolk
    Country:
    United Kingdom
    Shower pump? TV aerial booster? Towel rail?
     
  17. Licklieder

    Licklieder

    Joined:
    2 Oct 2010
    Messages:
    114
    Thanks Received:
    4
    Location:
    Surrey
    Country:
    United Kingdom
    Thats my current thinking - just need to get the damned halogen lights out to check. I honestly don't know how they were fitted - the size of the cutout is smaller that the size of the lights at the edge of the springs, and there are no grooves in the plasterboard to indicate where they were inserted.
     