    Looking to upgrade shower from broken 7.5kW. Trying to work out whether I have 6mm2 or 10mm2 cable in the current installation (it's connected to a 40A MCB). Can anyone tell from these pictures? Copper strands seems to be just over 1mm diameter and brown cable is about 6mm diameter.

    [​IMG]
    [​IMG]
     
  2. Sponsored Links
  3. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,148
    Thanks Received:
    1,273
    Country:
    United Kingdom
    If the earth conductors are rigid copper,not stranded ,the cable is not 10 mm²
     
    • Thanks Thanks x 2
  4. katheh

    katheh

    Joined:
    13 Jun 2011
    Messages:
    47
    Thanks Received:
    4
    Location:
    London
    Country:
    United Kingdom
    Thanks @terryplumb . Earth cable looks like this so I guess it is indeed 10mm2.

    [​IMG]
     
  5. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    8,421
    Thanks Received:
    902
    Location:
    Essex
    Country:
    United Kingdom
  6. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,148
    Thanks Received:
    1,273
    Country:
    United Kingdom
    It would appear so ,but examine the outer grey sheath ,the cable size should be embossed into it.
     
    • Thanks Thanks x 1
  7. katheh

    katheh

    Joined:
    13 Jun 2011
    Messages:
    47
    Thanks Received:
    4
    Location:
    London
    Country:
    United Kingdom
    I can't get to that very easily unfortunately
     
  8. Sponsored Links
  9. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,148
    Thanks Received:
    1,273
    Country:
    United Kingdom
    What KW rated shower are you thinking of installing ?
     
  10. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,608
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    I agree that it almost certainly is 10mm², but if you wanted to be absolutely certain (without being able to see/read the sheath) and had a micrometer or vernier caliper, you could count the cores and measure the diameter of one of them - and then calculate to total cross-sectional area.

    Do I take it that you cannot see (hence read) the sheath at either end of the cable, and/or are you not comfortable looking inside the CU?

    Kind Regards, John
     
    • Thanks Thanks x 1
  11. katheh

    katheh

    Joined:
    13 Jun 2011
    Messages:
    47
    Thanks Received:
    4
    Location:
    London
    Country:
    United Kingdom
    10.8kW ideally or the highest possible without the disruption of changing the cable (current shower is 7.5kW). I believe the MCB will need to be changed to 50A. I'll get an electrician in to do it but helpful to know in advance what I currently have. Plumber assumed cable would be 6mm2 without even looking and told me to get that upgraded to 10mm2 first.
     
  12. katheh

    katheh

    Joined:
    13 Jun 2011
    Messages:
    47
    Thanks Received:
    4
    Location:
    London
    Country:
    United Kingdom
    Yeah, just been searching the house for a micrometer or vernier caliper and have concluded I don't have one! Cable goes straight into the ceiling by the shower and is boxed in above the CU. I could get in the crawl space in the eaves above the CU assuming all the cables go up there but might be tough to work out which is which. How would I look inside the CU?
     
  13. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,608
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    As has been said, it almost certainly is 10mm² cable.

    However, even if it were 6mm², if installed with 'Method C', that would have a current-carrying-capacity of 47A. A "10.8 kW" shower almost certainly means 10.8 kW at 240V, which corresponds to just over 43A at 230V. Hence, if it were 'Method C', then it would seem that 6mm² cable on a 45A MCB would be adequate.

    Kind Regards, John
     