Baxi HE133 Boiler Fault Finding Help Please

Joined
8 Apr 2008
Messages
10,707
Reaction score
2,703
Location
Essex
Country
United Kingdom
You sure the diagram aligns with the one you posted ? if its got a molex connector it should be the next diagram down on the pdf.
 
Sponsored Links
Joined
27 Nov 2016
Messages
8
Reaction score
0
Country
United Kingdom
Ahhaa, I looked at Fig 4 for the honeywell valves and agree with you logic on SPST so thought I had better double check the actuator fitted to the boiler and its different than the spare I acquired (which is Fig 3 and shows SPDT config), it is configured for SPST control (Pic below)

IMG_0555.JPG


So excellent spot ! thanks

Now back to the fault, could it be the Actuator as it should have permanent 240v on pin 3 and 240v as well on pin 6 when CH demand is on. This is what I have measured on the boiler !

Thanks
 

Attachments

  • IMG_0556.JPG
    IMG_0556.JPG
    91.9 KB · Views: 78
Joined
8 Apr 2008
Messages
10,707
Reaction score
2,703
Location
Essex
Country
United Kingdom
So your looking at changing the actuator as the pcb is sending what its supposed to.
 
Sponsored Links
Joined
27 Nov 2016
Messages
8
Reaction score
0
Country
United Kingdom
Yeah thanks, back to the 1st item i changed - good lesson learnt to check if the replacement part is the same as the one removed. Will pick up a new actuator tomorrow from the local gas merchant and try tomorrow night.

Yes AGAS going round in circles one could say, but at least I now now how the system works ;)

Thank you for you support gents.
 

DP

Joined
10 Dec 2003
Messages
15,660
Reaction score
3,538
Location
Glasgow
Country
United Kingdom
Figure 3. the first one you posted , cant see how you can have 240 on both brown and black with a spdt relay.

When relay operates, cam eventually breaks the drive and other contact is made completing the circuit for drive home when relay releases. Am I missing something?
 
Joined
8 Apr 2008
Messages
10,707
Reaction score
2,703
Location
Essex
Country
United Kingdom
Relay on the boiler pcb not the relay in the actuator head.
 