Baxi Solo 3PF 60 Cuts out after 1 hour - 1 day

Joined
11 Mar 2004
Messages
4
Reaction score
0
Country
United Kingdom
Help!, my boiler Baxi Solo 3PF is about 4 years old and now cuts out when it feels like it, the little orange lights on the boiler all stay lit up the fan continues to operate as does the pump but no flame at the boiler. I can then turn off either the electrics or turn down the rotary control on the boiler and everything restarts nicely and may continue to work for 1 day or 1 hour. Any help or guidance would be much appreciated. Steve
 
Sponsored Links
ok

If fan is running but there is no sparking at electrode trying to light pilot,
then I would go air pressure switch
 
Sponsored Links
It was a cut rubber tube leading to the pressure switch, not obvious until taken off small slits on it probably from assembly causing the pressure switch to act up.
 