It suggests to me that your cylinder heat coil transfer rate is too low and probably your boiler is over rated for the house!
Do you really have a whole house heat loss of 22 kW ???
AND 22 kW of radiator output?
You say its a foamed cylinder but the old yellow ones had a pretty miserly heat coil and if thats a bit scaled up then its not surprising that it cannot absorb 8 kW when the differential is only 15°C.
Change cylinder, get a lower power boiler, increase the differential or just ignore the cycling!
Tony
Do you really have a whole house heat loss of 22 kW ???
AND 22 kW of radiator output?
You say its a foamed cylinder but the old yellow ones had a pretty miserly heat coil and if thats a bit scaled up then its not surprising that it cannot absorb 8 kW when the differential is only 15°C.
Change cylinder, get a lower power boiler, increase the differential or just ignore the cycling!
Tony