Discussion in 'Plumbing and Central Heating' started by David89, 6 Mar 2021.

  1. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    Sounds like too much secondary air for cold start.
    Really needs someone there with an oil pressure gauge connected to prove if its a fuel problem.
     
  2. Sponsored Links
  3. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    I've had someone out twice. I think he's as miffed as me...
     
  4. BoilerBob

    BoilerBob

    Joined:
    21 Feb 2020
    Messages:
    216
    Thanks Received:
    46
    Country:
    United Kingdom
    Seems very likely that if an oil gauge is put on the oil pump that you will see that perhaps this problem can be solved by installing a tiger loop this will get
    rid of excess air and hopefully solve the problem and if done right will keep the oil pump in flood condition so as to make sure the burner fires up first time. Bob
     
  5. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    That's going to be our next option
     
  6. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    What is the nozzle size....oil pressure and combustion readings.
     
  7. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    Terry. I can find out the nozzle size, he just replaced the one that had been working fine since the last service but I don't know the exact readings he got from his flu/gas analyser. He did mention he was struggling to get the air 'low enough' as the air adjuster was set to its minimum setting.
     
  8. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    What size is the nozzle.? Also Boiler output. Minor 1 burners do not normally need modification above 50000 btu.
    Below that a low output backplate and tube were available, But if the burner was supplied with the Boiler it should be correct Unless it is oversized and down rated.
     
    Last edited: 11 Mar 2021
  9. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    I can't get the nozzle size until I go round there Saturday. The thing is, this set up has been working and serviced regularly for probably 18 years. Nothing in the set up has been changed. I will forward the nozzle size ASAP
     
  10. Sponsored Links
  11. Burnerman

    Burnerman

    Joined:
    7 Feb 2008
    Messages:
    23,143
    Thanks Received:
    4,500
    Location:
    Northumberland
    Country:
    United Kingdom
    Can you confirm two things, if possible?
    1) are the baffles and flueways in the boiler clear?
    2) check for any air leak between the burner flange and the boiler.....look for soot / rust deposits in that area.
    John :)
     
  12. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    It has worked without problem for many years so a Tigerloop should not be needed Bob !!
     
  13. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    A 20 year old Warmflow without a few soot and rust deposits would be a difficult beast to find !!!:ROFLMAO::ROFLMAO:
     
    • Like Like x 2
  14. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    I can confirm, The whole flu and baffles were completely brushed, scraped and vaccumed clean on the first visit by the engineer in Early January 2021 when this problem started. He then checked and changed the oil pump, nozzle and optical sensor. The boiler was then checked for correct combustion. He did mention then, he was struggling to get the air 'low enough' but got the burner running and left happy. All worked well for a few days, then this, first start off the timer issue started. It starts and runs trouble free until the second timed start in the evening, when it fails to start and locks out....
     
  15. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,132
    Thanks Received:
    510
    Location:
    Shropshire
    Country:
    United Kingdom
    I'm still with the overaired camp. Many Minor 1 burners run at minimum setting, particularly if only fitted with 0.5 nozzles or thereabouts. Full spec of boiler and combustion settings etc are needed.
    Once started, as the day gets warmer, then the setting is less critical.
    Is this a balanced flue boiler?
     
  16. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    Is there a fookin echo in here !!:whistle:;)
     
  17. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    I think the nozzle is a 0.50 60° EH but would need to confirm
     