    hello I have a camray 5 oil burner,,,and its just started doing this,,,it fires up heats the rads till they hot then stops,,,then when they cool right down it starts heating them again and so on,,,same with the hot water,,,it fires up on morning and heats the water till its red hot,,,then a few hours later when the water has cooled and its only warmish the boiler wont fire again to heat it back up to hot,,,once the water has gone cold it will fire up again no problem and heat the water till its red hot again,,,its as if some kind of temperature sensor is faulty???,,,ive just had a new circulating pump fitted a few weeks ago if that means anything???
     
    Last edited: 26 Sep 2015
  2. Boilerman2

    Boilerman2

    Joined:
    10 Jun 2009
    Messages:
    5,225
    Thanks Received:
    1,015
    Location:
    Suffolk
    Country:
    United Kingdom
    What Model Camray 5 is this is a Combi per chance?? could be that the pump is stopping with the burner I've seen this a few times usually down to a failed auxillary switch in the diverter valve actuator
     
  3. Sponsored Links
  4. sonofrob

    sonofrob

    Joined:
    4 Jan 2014
    Messages:
    168
    Thanks Received:
    3
    Location:
    Durham
    Country:
    United Kingdom
    it is a camray combi 70a mate...
     
  5. MrTherm

    MrTherm

    Joined:
    20 Dec 2013
    Messages:
    148
    Thanks Received:
    36
    Country:
    United Kingdom
    Sounds like your control stat is not working so the boiler is relying and working on the limit stat alone, both stats are wired in tandem. Should the limit stat ever trip to prevent overheating, it needs a cool down period before a reset can be enabled.

    To test that the control stat is working, ensure the limit neon indicator is lit then with system calling for heat check for live voltage present at the L1 terminal of the burner socket. No live at this terminal indicates control stat is not working.

    Obviously the control stat should always be set to a lower temp than the limit stat to prevent nuisance resets such as you are experiencing.

    regards
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page