    Hi, I've been slowly renovating my 1960s chalet bungalow and now want to move a radiator in my dining room. Whilst there is no flooring down i took the opportunity to map out the existing pipework. Would someone be kind enough to look at the attached diagrams and advise if anything else needs changing to make a more efficient system. Upstairs pipework is more or less inaccessible at the moment so looking at the groundfloor for the time being.

    The change i mentioned is to put vertical radiators in the lounge and dining room, whilst moving the dining room rad from the outside wall to the internal wall, basically shortening the pipework

    The boiler is located at the end of the thicker 22mm pipe, the rest is 15mm

    Thanks
     

    Attached Files:

  2. Servotech

    Servotech

    Joined:
    19 Nov 2009
    Messages:
    370
    Thanks Received:
    50
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    It's a standard two pipe central heating system with each radiator return going direct to the boiler.
    Vertical radiators are nowhere near as efficient horizontal ones, so do bear this in mind especially if you like to be toasty warm in winter!
     
    • Thanks Thanks x 2
    • Like Like x 1
  3. Sponsored Links
  4. Madrab

    Madrab

    Joined:
    4 Oct 2012
    Messages:
    8,572
    Thanks Received:
    2,483
    Location:
    East Renfrewshire
    Country:
    United Kingdom
    +1, you need to be careful to check insulation levels, windows type etc. Vertical column radiators can be anything up to 50% less efficient at heating a space than normal convecting radiators. Don't just go by the radiator output.

    Column rads work at around 70% radiation and 30% convection whereas normal radiators work by 90% convection and 10% radiation, therefore they are much more efficient at space heating.
     
  5. MeldrewsMate

    MeldrewsMate

    Joined:
    27 Jan 2010
    Messages:
    1,125
    Thanks Received:
    282
    Location:
    Buckinghamshire, Darn Sarf
    Country:
    United Kingdom
    I can't work out where your boiler is in that system sketch, but from what info you have given it seems that multiple rads are fed from a pair of 15mm pipes. I suggest that a maximum of 15,000 btu/hr is fed from a 15mm pipe pair, less if there are long runs, so consider upgrading the distribution pipes to 22mm so that only two rads are fed from any 15mm pair. Doing it this way will keep flow velocities from going too high and creating system noise.

    I also suggest that ALL radiators are 100% efficient, and that Madrab and Servotech are refering to their effectiveness. As a word of warning, manufacturers usually quote their rads' outputs for quite high flow temperatures (delta T = 50), which means their average temperature is 50C higher than the room. If you want the room to be at 20C then you'll be looking at flow temps of 75C and return temps of 65C (or 77/63, etc). The current trend is towards lower flow temps, so larger rads will build in some modicum of future-proofing.
     
  6. Sponsored Links
  7. TonyS82

    TonyS82

    Joined:
    1 Mar 2011
    Messages:
    96
    Thanks Received:
    2
    Location:
    Essex
    Country:
    United Kingdom
    Thanks for the reply. Sorry i missed off the boiler, heres an updated layout if it helps. The boiler is in yellow located in the kitchen and has 22mm flow and return until the first elbow.
    The rad on the far right is in an older extension and tees off the pipe in the living room. This has a new insulated flat roof and insulation in the floor. The rest of the house has suspended timber floors.
    When i get round to doing the kitchen i was going to take the floor up and run new pipes for the rad inthe extension straight off the end of the 22mm flow and returns.
    By distribution pipes do you mean the two centeal pipes running through the middle?
     

    Attached Files:

  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page