Checking gas supply capacity

Joined
10 Nov 2007
Messages
162
Reaction score
4
Country
United Kingdom
Is it possible to check the gas supply capacity in advance of fitting a boiler?


A site currently runs electric storage heaters from a 100A 3ph supply. (70KVA)

The site has a U6 gas meter (6 m^3/hr nominally; previously only used for gas tumble dryers) and we'd like to convert to gas.

Maybe the supply from the main can flow enough gas to deliver 6 m^3 @ 21 mbar after the regulator. Maybe the supply from the main can't.


-How is this checked prior to deciding to install boilers?
-Who checks it?

-Is there a service level guarantee on a gas supply? (are the distributors obliged to deliver 6m^3/hr; who pays if not?)


Thanks,
 
Sponsored Links

DP

Joined
10 Dec 2003
Messages
15,546
Reaction score
3,497
Location
Glasgow
Country
United Kingdom
These are things you do not need to worry about ;)

You installer, if he is gas Safe, will know what to do.
 
Joined
10 Nov 2007
Messages
162
Reaction score
4
Country
United Kingdom
Unhelpful.


Most gas safe people seem happy to fit the boilers then check afterwards, with no concern for impact on timetables.


For water I'd ask for a dynamic pressure check. What's the equivalent in gas lingo please? I want the check done in advance of planning all the works, not something that throws a spanner in the works.


(Wednesbury if anybody would like to quote for the job)
 
Joined
5 Apr 2014
Messages
727
Reaction score
126
Location
London
Country
United Kingdom
Someone needs to do a pipe sizing calculation to ensure the pipe is of a sufficient diameter taking into account the length, bends, elbows and other appliances that may be drawing off gas at the same time.
I don't know what engineers you use but I for one don't just fit a boiler and worry about it afterwards. I try to avoid call backs from unhappy customers as I could be elsewhere earning money.
 
Joined
10 Nov 2007
Messages
162
Reaction score
4
Country
United Kingdom
Pipework after the meter is not a problem.

I'm talking about the supply to the meter: is the main adequate? Many aren't. How do you check?
 
Joined
10 Nov 2007
Messages
162
Reaction score
4
Country
United Kingdom
Are they obliged to provide 21 mbar @ 6 m^3/hr?

Worst case scenario, what the usual turnaround time?
 
Joined
1 Jul 2007
Messages
56,034
Reaction score
9,554
Location
Hertfordshire & London
Country
United Kingdom
No - it is a lower pressure, but I can't remember what.


Turn around time? Months. Working on one at the moment. Order for a new supply went in in April.

Not sure if it has been finished yet. That was running a new pipe 6 metres across a side road.


Admittedly it was a 3" supply for carrying 17 cubes though.
 
Sponsored Links
K

keego

Your maximum load on a U6 would be 64.6kw, that's not taking into account your loss on the pipework.
 
Joined
10 Nov 2007
Messages
162
Reaction score
4
Country
United Kingdom
No - it is a lower pressure, but I can't remember what.

12.5 mbar apparently. Enough that your hob doesn't blow out and cause a safety issue; not enough to guarantee you're able to run your gas appliances though.

Apart from WB (TB 0040) is there anybody else that'll allow commissioning below 21 mBar?


Turn around time? Months. Working on one at the moment. Order for a new supply went in in April.

Not sure if it has been finished yet. That was running a new pipe 6 metres across a side road.

That's the type of delay I feared. Looks like there's no way to check flowrates beforehand though so flag as a risk and aim to commission ASAP.
 
Joined
10 Nov 2007
Messages
162
Reaction score
4
Country
United Kingdom
Not in recent living memory; it's been capped for a decade.


We'll find out in due course of this meter can supply 6m^3/hr. No gas safe people I've called can answer this question without there being existing equipment hooked up to it. (there is none)
 
Joined
4 Jan 2014
Messages
1,271
Reaction score
183
Location
Lanarkshire
Country
United Kingdom
Unhelpful.


Most gas safe people seem happy to fit the boilers then check afterwards, with no concern for impact on timetables.


For water I'd ask for a dynamic pressure check. What's the equivalent in gas lingo please? I want the check done in advance of planning all the works, not something that throws a spanner in the works.


(Wednesbury if anybody would like to quote for the job)

It think it would be more helpful if you provided more details rather than being abusive to one of the highly respected members here.

You clearly have gone in to some detail of the gas supply, but failed to divulge the obvious: like size of the building, rough date of construction & type of building.
 
Joined
9 Apr 2008
Messages
668
Reaction score
65
Location
London
Country
United Kingdom
Well worded Sir Richard.
Hope others will note and do the same.
 
Joined
14 Nov 2007
Messages
1,660
Reaction score
256
Location
Buckinghamshire
Country
United Kingdom
You need to work out what size gas boiler / gas rate you need for heating / hot water system.
And you need to add gas cooker gas rate as well if fitted.

Gas rate size is depend on heat output from boiler.

Your gas safe installer will work out what gas rate need for a safe working condition.

If the gas rate is higher than what the U6 can supply, you need to upgrade to U10 or U16 depend on gas rate requirement for your installation.

Daniel.
 