Discussion in 'Plumbing and Central Heating' started by pemba, 5 Jan 2016.

  1. pemba

    pemba

    Joined:
    22 Apr 2010
    Messages:
    25
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Hi there the highest radiator in my central heating system was cold so i knew it needed bleeding. The system is powered by a Valiant Combi boiler and the pressure was low (0.5), so i topped it up as recommendedon several posts, to about 1.4, whilst bleeding the radiator. Now when the boiler runs the pressure increases to above 2.2 (not too sure how high it would go as i'm switching it off when it gets to 2.2). After reading several other posts i'm now not so sure that i've used the correct "taps" for topping up the pressure.

    I intend to let the system cool down and then release the pressure back to where it was and run the system again. Any advice on what could have gone wrong? is the increase in pressure normal? am i worrying unduly?
     
  2. Sponsored Links
  3. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,627
    Thanks Received:
    2,382
    Location:
    Londonderry
    Country:
    United Kingdom
    You can get a pressure rise of up to 2.0 bar, if the pressure reaches above it's expected value the PRV should activate.
    How large is the installation.
     
  4. pemba

    pemba

    Joined:
    22 Apr 2010
    Messages:
    25
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Many thanks for the respons.
    It is a reasonably large semi-detatched house with 4 bedrooms and 2 reception rooms, so not massive.
    I've dropped the pressure to 0.8 and put the heating back on and it went up to 2.6 before I lost my bottle and switched the heating off again!
     
  5. ChewChew

    ChewChew

    Joined:
    5 Jan 2016
    Messages:
    29
    Thanks Received:
    0
    Country:
    United Kingdom
    It could be an issue with the expansion tank. Its interesting to note you didn’t have this problem before you bled the cold rad. It might be the rad full of air was acting like an expansion tank which prevented the pressure build up.
    Things to check – blocked hose to expansion tank, tank needs repressurising or replacing.
     
  6. pemba

    pemba

    Joined:
    22 Apr 2010
    Messages:
    25
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Thanks ChewChew that is an interesting suggestion.
    I hate it when things apparently happen for no associated reason but the radiator acting as you suggest could make sense. Problem i've got now is that trying to check anything like that is probably way beyond my ability. I've got the system running now and it is sitting about 2 Bar above the normal when it is running fully hot (central heating). This is obviously outside of the Green area but also below the Red area. As i mentioned before it is a relatively large system heating 15 radiators - do you think it acceptable that it has a pressure differential of 2 Bar as previously suggested by PrenticeBoyofDerry?
     
  7. Sponsored Links
  8. martyndc88

    martyndc88

    Joined:
    26 Apr 2009
    Messages:
    1,089
    Thanks Received:
    309
    Location:
    South Glamorgan
    Country:
    United Kingdom
    sounds like the expansion vessle is flat/faulty. you should get it checked out
     
  9. MANDATE

    MANDATE

    Joined:
    6 Mar 2003
    Messages:
    2,328
    Thanks Received:
    134
    Location:
    Manchester
    Country:
    United Kingdom
    The increase in pressure is related to the size of the vessel and the " air charged ".
    These dictate the volume of air that is available to be compressed.
    A large system holding more water would need a larger vessel with larger volume.
    Initially before any water is pressurised the 'air' side needs to be pre charged to about 1bar.
    This forces the diaphragm to the water side and the volume of air available for compression is at it's Max.
    If the vessel was not air charged the diaphragm would move to the opposite end of the vessel with no volume of air to compress.
    Most problems relate to the partial loss of air pressure and it's not too difficult to correct it.
    There is one important condition and that is ensuring there is no water in the vessel where air should be.
    To ensure this the water side need's to be open to atmosphere.
    Note a blocked pipe from vessel would have similar effect
    Adding another vessel would increase the total capacity.
    Normally most systems are set about 1bar air pressure followed by 1bar water pressure.
    The 1bar water pressure should rise by 1 or 1.5 bar but should not reach 3.
    If it does reach 3 then the pressure relief valve opens, the excess water is discharged and the valve closes and the pressure drops.
    Also note that prvs once opened don't always seal correctly, leaving a small leak and another problem to deal with
    ?
     
  10. mcmoby69

    mcmoby69

    Joined:
    19 Jun 2011
    Messages:
    6,802
    Thanks Received:
    2,314
    Location:
    Lancashire
    Country:
    United Kingdom
    expansion vessel charge is usually checked when serviced. or 'should' be. when was it last serviced?
     
  11. pemba

    pemba

    Joined:
    22 Apr 2010
    Messages:
    25
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Guys loads of brill information, really appreciate your help, and i'll get on the case tomorrow and let you know the outcome.
     
  12. pemba

    pemba

    Joined:
    22 Apr 2010
    Messages:
    25
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Guys as you suggested the expansion vessel was at fault. Simple job (for a professional!) to relieve the water pressure, top up air pressure and repressurise the water side. System now sitting at 0.8 rising to 1 when operating.

    Many thanks for all the information.
     
  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page