    Just wired up today.
    Couldn't get hot water to turn off unless using cylinder stat.
    Constant 240v on pin 6 of heat link despite no demand on stat.
    Linked 240v over from L pin to pin 2 (CH) and pin 5 (HW).
    Guessing relay stuck on HW.

    Sanity check please.
     
  2. Sponsored Links
  3. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,500
    Thanks Received:
    9,699
    Location:
    Lanarkshire
    Country:
    United Kingdom
    which boiler ? S plan or Y plan ?
     
  4. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,933
    Thanks Received:
    1,291
    Location:
    Potters Bar
    Country:
    United Kingdom
    Worcester (greenstar I think, combi with internal panel clock).
    Now using it as system boiler.
    S plan.

    Now thinking it might be the legionella setting on Nest?
     
  5. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,500
    Thanks Received:
    9,699
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Yes was going to suggest that, I have been caught out with that before, all Worcester condensing boilers are called greenstar, annoying I know, did you wire the two orange wires from the zone valves to the 240v room thermostat connection on the boiler ?
     
  6. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,933
    Thanks Received:
    1,291
    Location:
    Potters Bar
    Country:
    United Kingdom
    Yup. Both fire wires (oranges) from MCVs wired to LR (rad symbol) on the boiler control box.
    Have to be honest, all WBs look same to me... Just looked for the switched live in.
     
  7. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,500
    Thanks Received:
    9,699
    Location:
    Lanarkshire
    Country:
    United Kingdom
    a few posts, WB dont like using 5 core or close two 3 cores , but dont think this is your problem here, disconnect the ribbon on the inbuilt programmer on the boiler and see if you still have the same problem, could be a back feed from the boiler
     
    • Thanks Thanks x 1
  8. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,933
    Thanks Received:
    1,291
    Location:
    Potters Bar
    Country:
    United Kingdom
    Yeah... Also been thinking about built in prog being issue.
    BUT... having taken HW demand from pin 6 out of heat link AND perm live from pin 5 out of heat link, then reinserting perm live to pin 5... After few seconds, 240 reappears on pin 6...this is surely an issue internal to the heat link? I think! o_O
     
  9. Sponsored Links
  10. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,500
    Thanks Received:
    9,699
    Location:
    Lanarkshire
    Country:
    United Kingdom
    First rule of everything mate, disconnect all external controls and then re-connect one at a time, once you get the problem again take a step back and see what you have just done, I fit lots of Nest and Hives and have seen a few with connection issues, but never seen a stuck relay that wasnt caused by wiring it wrong and it fusing in the closed position, not saying it doesnt happen, just never seen it out of the box
     
    • Thanks Thanks x 1
  11. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,933
    Thanks Received:
    1,291
    Location:
    Potters Bar
    Country:
    United Kingdom
    Question.... Pin 6 can't get 240v from anything external! Even if fed clean voltage from pin 5 (from external non system source) relay from 5 to 6 should not be made unless Nest inner workings makes that switch!

    Been drinking and thinking :sneaky:
     
  12. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,500
    Thanks Received:
    9,699
    Location:
    Lanarkshire
    Country:
    United Kingdom
    so if any pin , external from anything is connected to another pin, could the live back feed ? hence why 2 port valves have end switches ?
     
    • Thanks Thanks x 1
  13. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,933
    Thanks Received:
    1,291
    Location:
    Potters Bar
    Country:
    United Kingdom
    I'll have at it again on Monday morning! (y)
     
  14. fezster

    fezster

    Joined:
    30 Jan 2013
    Messages:
    544
    Thanks Received:
    63
    Location:
    London
    Country:
    United Kingdom
    Is this a nest 3rd gen?

    If HW is on (or legionella programme), the thermostat will show a water drop icon. You can also turn off the legionella setting.

    Are you testing the 240V is on terminal 6 with a multimeter with the terminal not connected to anything (to rule out anything external making the cable live)?
     
    • Like Like x 1
  15. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,933
    Thanks Received:
    1,291
    Location:
    Potters Bar
    Country:
    United Kingdom
    Yes
     