    not strictly a DIY question but it follows a debate we were having at work today....

    whats people's opinions and experiences of the danger that could arise from these tests, i.e voltages/current appearing on earthed parts.

    whats the worst that could happen? is it safe to do so long as you have all bonding in place? and is there a risk of danger, particularly in industrial type installations, i.e lots of exposed metalwork/extraneous parts.

    comments welcome, cheers
     
  2. Sponsored Links
  3. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    GN3 states that an efli test should be carried out prior to an RCD test to check the requirements have been met.
     
  4. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,990
    Thanks Received:
    1,354
    Location:
    Leeds
    Country:
    United Kingdom
    My tester will not attempt to carry out an EFLI or RCD test if there is no earth present.
     
  5. holmslaw

    holmslaw

    Joined:
    12 Dec 2006
    Messages:
    5,841
    Thanks Received:
    400
    Country:
    United Kingdom
  6. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,362
    Thanks Received:
    1,308
    Country:
    United Kingdom
    I had this argument with an assessor who was supposed to be there to grill me on my procedures. I ended up grilling him...

    He insisted that before I carry out an EFLI test that I check MEB's were in place & made sure customers were not attached to anything metallic because of the large currents involved.With my tester, the currents are very low, so this was a red herring.
     
  7. ricicle

    ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,343
    Thanks Received:
    382
    Location:
    Gloucestershire
    Country:
    United Kingdom
    It is a strange one as you are looking for worst case in a Zs test but need to have MEBs connected to protect from possible shocks when testing so are providing parallel paths which will in theory give a lower reading.
    If the MEBs are ever taken out (metallic water pipe replaced with plastic) then the Zs will be higher.I like the method of calculation ( Ze +(R1+R2) ) as with correction factors gives you a more truthful indication of the Zs if the parallel paths should ever change (Unless your Ze is ever likely to change with network alterations)...........aaaarrrgggghhh :LOL:

    Another situation is like in the factory I work in.Where you have several large SWAs feeding bus-panels (.4 x 4core for anyone who's used to imperial sizes) These have no seperate earths ran so rely on the armouring.The SWA is made into the spreader boxes bolted on to the switch panels which is bolted on to an angle iron framework/factory steelwork/lattice of trunking etc so it is nigh on impossible to remove parallel paths albeit the amount of steelwork is so intense that adding/removing trunking/pipework will probably have a negligible effect on the R2 part of the loop.

    I'm mumbling now.......... :oops:
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page