Electric Oven

Discussion in 'Electrics UK' started by rglister, 13 Nov 2004.

This topic originated from the How to page called Installing a cooker hood.

  1. rglister

    rglister

    Joined:
    13 Nov 2004
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    If I install a separate SPUR for a fitted electric cooker, does it need an FCU in the kitchen?
     
  2. Sponsored Links
  3. breezer

    breezer

    Joined:
    3 Jan 2003
    Messages:
    23,324
    Thanks Received:
    30
    Location:
    Sussex
    Country:
    United Kingdom
    an electric cooker requires its own circuit and cooker connection unit, also 6mm cable which wont fit / too much for an fcu
     
  4. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Possibly even 10mm² cable....
     
  5. fred hiscock

    fred hiscock

    Joined:
    7 Nov 2005
    Messages:
    1
    Thanks Received:
    0
    Location:
    Devon
    Country:
    United Kingdom
    I am fitting an electric hob and oven. I am providing a 6mm spur to each direct from the consumer unit. I have a suppliers spec (20 amp oven 30 amp for the hob) for the switches / breakers at either end of the cables. My question is how long can I make each spur. I guess I would like them about 25 metres linear each. Is this ok. How much further could I take them if necessary? Regards Fred
     
  6. JayS

    JayS

    Joined:
    25 Feb 2004
    Messages:
    127
    Thanks Received:
    1
    Country:
    United Kingdom
    rglister's title says oven...topic says cooker...

    If it's a built in oven consider the following. What's the rating of the oven? If it's less then 3kW it'll do nicely in a 13A socket. :)

    Assuming this is the case and that you are running a spur off the ring main I think a 13A FCU is to be recommended but it's not a requirement I believe.

    If it's a cooker as breezer says.

    Also this falls under part P as we all know... :rolleyes:
     
  7. Steve

    Steve

    Joined:
    15 Apr 2005
    Messages:
    16,497
    Thanks Received:
    244
    Location:
    Yorkshire
    Country:
    United Kingdom
    no it wont fall under part p, work started in nov04
     
  8. Sponsored Links
  9. Gary0

    Gary0

    Joined:
    30 Sep 2005
    Messages:
    159
    Thanks Received:
    0
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Umm ... just intrigued. So it's when the work started that's important for Part P ? Not when it finishes ? (Please, yes/no if possible, rather than link to part P, would be much appreciated. Thanks)
     
  10. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Ah - but was he replying to the latest addition?

    Those aren't spurs, they are circuits, and notifiable to LABC.

    http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html

    Also, you need to read, and come to understand this: http://www.tlc-direct.co.uk/Book/4.3.1.htm so that you can show LABC that you've done it properly. You'll also need to acquire the necessary test equipment.

    No, but seriously - if you do plan to comply with the law, you will need to do it competently, even with a cooperative LABC who do what they are supposed to. If you've got one of the stroppy ones, you'll need to be on very firm ground if you are going to argue with them....
     
  11. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    For electrical only work, it used to be, but that window has now closed. (April 05).

    For general buildng work, the issue of whether or not compliance with Part P has to be added in can be determined from this:

    [​IMG]
     
  12. Gary0

    Gary0

    Joined:
    30 Sep 2005
    Messages:
    159
    Thanks Received:
    0
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Ah, thanks. Thought that sounded to good a loophole to have been overlooked :)
     
  13. JayS

    JayS

    Joined:
    25 Feb 2004
    Messages:
    127
    Thanks Received:
    1
    Country:
    United Kingdom
    Yes, you were able to start work before 1st of January 2005 and finish it before the 1st of April without having to bother with part P...but if it's not finished yet then it falls under part P...

    ban-all-sheds, any circuits going into a kitchen would also be effected (as well as being notifiable to LABC) by part P I presume since they would be a fixed installation?

    Learn to love part P... ;) :rolleyes:
     
  14. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Yup.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page