If I install a electric shower in a downstairs cloakroom can i take the power supply from the ring with a fused spur or do I need to wire it completely seperate. :LOL:
 
Sponsored Links
Joined
5 May 2007
Messages
119
Reaction score
0
Country
United Kingdom
Its probably easier to run it separate if the consumer unit is there in the cloakroom

PS don't forget the the label warning of 2 different wire colours :D
 
O

oompah

No the consumer unit is away from the cloakroom about 7 yards. :LOL:
 
Joined
16 Feb 2007
Messages
11,795
Reaction score
480
Location
West Midlands
Country
United Kingdom
oh good gods..

a shower takes more power than a ring can supply..

you will need to run 10mm² cable back to the CU and install a suitable MCB and RCD ( or RCBO which combines both into one. )

this is notifiable work as a shower makes it a bathroom and is covered by Part P of the building regulations..

you need to tell your local authority building control IN ADVANCE of starting the work..


might just be easier and cheaper in the long run to get a qualified and part P registered electrician in..

also, lazygit, if it's a cloakroom then the CU had better not be in there because it sure as hell would be in the zones..
 
Sponsored Links
O

oompah

ColJack said:
oh good gods..

a shower takes more power than a ring can supply..

you will need to run 10mm² cable back to the CU and install a suitable MCB and RCD ( or RCBO which combines both into one. )

this is notifiable work as a shower makes it a bathroom and is covered by Part P of the building regulations..

you need to tell your local authority building control IN ADVANCE of starting the work..


might just be easier and cheaper in the long run to get a qualified and part P registered electrician in..

also, lazygit, if it's a cloakroom then the CU had better not be in there because it sure as hell would be in the zones..
Thankyou I didn`t think it would be that easy.
 
Joined
21 Oct 2004
Messages
19,558
Reaction score
25
Country
United Kingdom
lazygit said:
Its probably easier to run it separate if the consumer unit is there in the cloakroom
Tip: when you don't have the slightest, foggiest, slimmest, tiniest, faintest, most tenuous grasp of the subject you're advising on, then it's time to shut up.
 
Joined
1 May 2006
Messages
919
Reaction score
1
Country
United Kingdom
should'nt it be confirmed first that its a electric shower rather then a power shower :rolleyes:
 
Joined
16 Feb 2007
Messages
11,795
Reaction score
480
Location
West Midlands
Country
United Kingdom
electric shower stated, not shower pump etc, so the advice given was based on that..
 
O

oompah

ColJack said:
electric shower stated, not shower pump etc, so the advice given was based on that..
definitely a electric shower, to far from hot water tank .
 
O

oompah

Softus said:
lazygit said:
Its probably easier to run it separate if the consumer unit is there in the cloakroom
Tip: when you don't have the slightest, foggiest, slimmest, tiniest, faintest, most tenuous grasp of the subject you're advising on, then it's time to shut up.
So what do you think is the best idea?
 
O

oompah

Softus said:
lazygit said:
Its probably easier to run it separate if the consumer unit is there in the cloakroom
Tip: when you don't have the slightest, foggiest, slimmest, tiniest, faintest, most tenuous grasp of the subject you're advising on, then it's time to shut up.
 
Joined
21 Oct 2004
Messages
19,558
Reaction score
25
Country
United Kingdom
oompah said:
So what do you think is the best idea?
WTF?

ColJack has already told you everything you need to know and do - why are you still asking? :!:
 
O

oompah

Softus said:
oompah said:
So what do you think is the best idea?
WTF?

ColJack has already told you everything you need to know and do - why are you still asking? :!:
How do you know its everthing i need to know?
 
Joined
5 May 2007
Messages
119
Reaction score
0
Country
United Kingdom
Softus said:
Tip: when you don't have the slightest, foggiest, slimmest, tiniest, faintest, most tenuous grasp of the subject you're advising on, then it's time to shut up.

Dude, I was taking the p155 because the I found the spur issue funny. :rolleyes:
 