With a fixed outlet the voltage must be no less 11.5 volt below incoming voltage (5%) but with an extension lead the voltage where RCD protection is given can drop to silly values and still comply. Most sockets needed a ELI of 1.44 now less with amendment 3 and that relates to volt drop 230 - 13A x 1.44Ω gives 211 volts. But with RCD protection an extension lead can still comply when volt drop means only 100 volt although that is being silly.
However fridges and freezers have for years had a problem, if the volts drops too much, on start before the motor has got to speed the pressure can build up to a point where the motor stalls and the overload disconnects the supply, it will retry once cooled, but if it can't start very quickly the overload is damaged, so most freezers and fridges state do not use an extension lead.
I would guess the label was for a fridge or freezer and has been stuck on a fan in error?