FENSA regulations?

Discussion in 'Plumbing and Central Heating' started by snico, 20 Sep 2017.

  1. snico

    snico

    Joined:
    28 Aug 2004
    Messages:
    2,533
    Thanks Received:
    11
    Location:
    Cheshire
    Country:
    United Kingdom
    Hi all, not posted here for a long time but in need of some advice that i'm struggling to find online

    I have a property that I am now renting out, which used to be my main residence

    I had a gas safe engineer out today to carry out a gas safety certificate, he has found that the bathroom window opening is less than 300m from the wall heater flue/vent

    The windows in the house where installed by Safestyle approx. 14/15 years ago.

    My question is, FENSA states that Open flue appliances affected by the window/door replacement will be checked for adequacy of combustion air supply. At the time of having the windows replaced, did this regulation still apply?

    Would Safetyle have not mentioned this when recommending the windows, or would they have issued a FENSA certificate?
     
  2. Sponsored Links
  3. Nige F

    Nige F

    Joined:
    28 Jun 2005
    Messages:
    21,203
    Thanks Received:
    1,741
    Country:
    United Kingdom
    I think you're confusing gas regs with window regs. The distance of the flue to *opening* window is a gas reg.
     
  4. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    33,921
    Thanks Received:
    4,606
    Location:
    West Mids
    Country:
    United Kingdom
    ... is not the same as the flue being close to an opening.

    In any case, this gas reg can not be applied retrospectively
     
  5. snico

    snico

    Joined:
    28 Aug 2004
    Messages:
    2,533
    Thanks Received:
    11
    Location:
    Cheshire
    Country:
    United Kingdom
    I understand that, but the flue/vent was there long time before the window was fitted. Safestyle recommended the half open window to match existing windows, surely their own surveyor should have spotted there was a vent below the window and not recommended that type.

    The original window opened at the top, so vent was fitted well within regulations, the new window break those regultions, that's window surveyor fault surely?
     
  6. freddiemercurystwin

    freddiemercurystwin

    Joined:
    21 Jan 2007
    Messages:
    19,859
    Thanks Received:
    2,218
    Location:
    Devon
    Country:
    United Kingdom
  7. Sponsored Links
  8. DHFrames

    DHFrames

    Joined:
    12 Feb 2013
    Messages:
    512
    Thanks Received:
    69
    Location:
    Avon
    Country:
    United Kingdom
    Flues serving oil pressured appliances should be a minimum of 600mm away from any openable window
    300mm if a fix pane

    Flues serving gas appliances is 300mm
    150mm if a fix pane

    I think there are a few versions of this reg
     
  9. snico

    snico

    Joined:
    28 Aug 2004
    Messages:
    2,533
    Thanks Received:
    11
    Location:
    Cheshire
    Country:
    United Kingdom
    Safestyle where FENSA members

    After a phone call today to Safestyle, they have agreed they have made an error in the surveying of the property.

    They are sending someone out towards the end of the month to measure up and replace the window that they installed
     
  10. snico

    snico

    Joined:
    28 Aug 2004
    Messages:
    2,533
    Thanks Received:
    11
    Location:
    Cheshire
    Country:
    United Kingdom
    It is a gas appliance yes, and less than 300mm from the window opening, luckily they are going to replace it
     
  11. DHFrames

    DHFrames

    Joined:
    12 Feb 2013
    Messages:
    512
    Thanks Received:
    69
    Location:
    Avon
    Country:
    United Kingdom
    Or extend the flue the opposite way??
     
  12. snico

    snico

    Joined:
    28 Aug 2004
    Messages:
    2,533
    Thanks Received:
    11
    Location:
    Cheshire
    Country:
    United Kingdom
    Its not a directional flue, open ended.

    Only option would have been to lower the wall heater, which wasn't possible due to floor clearance, or change the window.
     
  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page