    Hi All,

    I've a question for gas safe engineers please.

    Just had a boiler service and the engineer nearly cut my supply and issued an ID because he found a "socket-formed" capillary soldered joint in the gas supply. (BTW I'm not sure if I have the correct name for this joint, but basically where you widened the end of a copper pipe using a "socket former" which can then be pushed over a pipe of the same size and soldered). He said only slip on copper fittings were permitted in gas pipework. As the "socket-formed" joint was installed by a previous gas safe engineer, I'm wondering if these fittings are indeed dangerous and illegal as suggested by the current gas service engineer.
     
  2. Sponsored Links
  3. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    IIRC they are fine as long as they are made properly.
     
  4. algas

    algas

    Joined:
    18 Oct 2008
    Messages:
    858
    Thanks Received:
    168
    Location:
    Devon
    Country:
    United Kingdom
    Iv'e made hundreds of this type of joint in the past & I think they are safer than a bought socket as there is only one soldered joint to leak, he's being a bit of a knoob.
     
  5. 45yearsagasman

    45yearsagasman

    Joined:
    14 Mar 2010
    Messages:
    6,094
    Thanks Received:
    1,093
    Location:
    Norfolk
    Country:
    United Kingdom
    Expanded joint, and just as good and cheaper than end feed. Oh I should add IMO. Show me the reg that says you can't use them. It's not common practice though.
     
  6. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    14,790
    Thanks Received:
    3,251
    Location:
    Glasgow
    Country:
    United Kingdom
    Probably a young wipper snapper who has never seen such a joint. :D
     
  7. RickMoore

    RickMoore

    Joined:
    3 Jan 2013
    Messages:
    380
    Thanks Received:
    64
    Location:
    Lancashire
    Country:
    United Kingdom
    If it's been made properly nothing wrong with making a join that way IMO. Stronger than using a coupler.
     
  8. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,380
    Thanks Received:
    9,628
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Afraid your engineer is talking absolute crap
     
  9. johnnie888

    johnnie888

    Joined:
    9 Oct 2013
    Messages:
    5
    Thanks Received:
    0
    Location:
    Bristol
    Country:
    United Kingdom
    Thanks for all the replies guys. I've since spoken to the original gas installer for the boiler, plus the gas board who came to fix the low pressure at my meter (17mb) today, and they all say these socket joints are fine too. The general consensus was the gas safe engineer who serviced my boiler today was trying for business by getting me to replace the gas pipework from the meter to the boiler.

    In the end he left me with an "At risk" notice saying there was a 2.5 Mbar fall in pressure over the length of the internal pipework, and that the pipework was inadequate. He wanted put 28mm all the way to the boiler (currently it is 28mm for about 4m, and 22mm for the remainding 8-10m up to the boiler). However, is this really "At risk", also considering that he measured the 2.5Mbar drop at a working pressure of 17Mbar at the meter (I did have low pressure at the meter which the gas board is now fixing), and not the correct working pressure of around 20Mbar? I assume the drop in pressure would be less at higher working pressures, although not sure on this I must say!
     
  10. Sponsored Links
  11. RickMoore

    RickMoore

    Joined:
    3 Jan 2013
    Messages:
    380
    Thanks Received:
    64
    Location:
    Lancashire
    Country:
    United Kingdom
    2.5 mbar drop is massive on those pipe sizes. How big is the boiler and are their any other appliances that need to be taken into account ?
     
  12. johnnie888

    johnnie888

    Joined:
    9 Oct 2013
    Messages:
    5
    Thanks Received:
    0
    Location:
    Bristol
    Country:
    United Kingdom
    Hi Rick,

    Boiler is vaillant ecotec 831. (DHW = 31kw; heating 24kw). Currently its the only appliance is the house. There was a gas cooker which I asked the service engineer to disconnect today as I am moving the kitchen. I do intend to have a new gas cooker in the new kitchen at some stage.

    To update the gas board now has 19 Mbar at meter, dropping to 14 on initial start up of the boiler. Tomorrow they will replace the 16mm supply pipe into my property hopefully giving me 21 mbar at the meter. I guess that should give me sufficient pressure at the boiler even if there was a pressure drop of 2.5mbar on the internal pipework.
     
  13. CBF

    CBF

    Joined:
    15 Oct 2012
    Messages:
    2,165
    Thanks Received:
    363
    Location:
    Hampshire
    Country:
    United Kingdom
    where did he test the pressure at the boiler ?
     
  14. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Nice to see engineers keeping abreast of manufacturer product updates ;)
     
  15. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    I agree that socket joints are actually stronger and safer than couplings.

    However, since they are made by the installer, it is my view that they are not permitted as they are not "manufactured for use on gas".

    It would be interesting to know what attitude Gas Safe takes!

    Anyone asked them?

    Tony
     
  16. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Yes. And my answer was based on that.
     
    • Thanks Thanks x 1
  17. sooey

    sooey

    Joined:
    10 May 2006
    Messages:
    11,971
    Thanks Received:
    889
    Location:
    Merseyside
    Country:
    United Kingdom
    A couple of years ago I fitted a boiler in my local gas safe inspectors house :eek:, he had a lot to do and only a couple of days so asked me to give him a hand.
    Anyway he had a socket formed joint on his gas pipe and wasn't too bothered about it. :LOL:
     