Discussion in 'Electrics UK' started by nick9one1, 12 Oct 2021.

  1. nick9one1

    nick9one1

    Joined:
    19 Jun 2021
    Messages:
    20
    Thanks Received:
    0
    Country:
    United Kingdom
    I have two bathrooms with a triple switch (extractor, lightswitch, fuse) and another separate switch for the opposite room light.

    I've replaced the old extractor with an timed humidistat expelair that draws 7.7w max.

    I'm going to combine the bathroom light and extractor, and remove the separate switch, moving it to a new smaller double bathroom switch as the image shows.

    My question is about the fuse. Is it still needed for a 7.7w extractor? If so is there an inline fuse I can install behind the switch?
    20211012_114356.jpg
     
  2. Sponsored Links
  3. opps

    opps

    Joined:
    16 Jun 2006
    Messages:
    5,173
    Thanks Received:
    817
    Location:
    London
    Country:
    United Kingdom
    • Thanks Thanks x 1
  4. nick9one1

    nick9one1

    Joined:
    19 Jun 2021
    Messages:
    20
    Thanks Received:
    0
    Country:
    United Kingdom
    Yes youre correct. Should have read the manual!

    Capture.PNG

    This makes it a little more complicated.
    I think I will have to install a separate 2 pole isolator near the floor outside the bathroom.
     
  5. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,442
    Thanks Received:
    4,201
    Location:
    Retired to:
    Country:
    Portugal
    It is up to you what you do but, if on the lighting circuit, the fan does not need a fuse nor an isolator.
     
  6. opps

    opps

    Joined:
    16 Jun 2006
    Messages:
    5,173
    Thanks Received:
    817
    Location:
    London
    Country:
    United Kingdom
    You might have to install a fused spur as well given that it specifies a 5 amp fuse...

    ___________ edit__________ submitted before reading EFL's post

    That said, by using an isolator, if it decides to start running on a particularly humid night, you can turn it off if you have an isolating switch- the humidistat is on the permanent live, and not the switched live.

    Oh, and don't forget to earth the 4 core cable at the supply side. The device does not need the earth but the cable should be earthed (just in case).
     
    Last edited: 12 Oct 2021
    • Thanks Thanks x 1
  7. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,195
    Thanks Received:
    555
    Location:
    London
    Country:
    United Kingdom
    His lights won’t be on a ring. Rings are for UK socket circuits.
     
  8. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,195
    Thanks Received:
    555
    Location:
    London
    Country:
    United Kingdom
    It doesn’t. It says MAX 5 amp fuse. It is wrong anyway as the fuse is to protect the cable not the fan which should be internally protected.
     
  9. opps

    opps

    Joined:
    16 Jun 2006
    Messages:
    5,173
    Thanks Received:
    817
    Location:
    London
    Country:
    United Kingdom
    Yeah, my bad. they are (typically) radial. I made the mistake of saying ring, when in reality, I should have used the words lighting circuit.
     
    Last edited: 12 Oct 2021
  10. Sponsored Links
  11. opps

    opps

    Joined:
    16 Jun 2006
    Messages:
    5,173
    Thanks Received:
    817
    Location:
    London
    Country:
    United Kingdom
    Sorry Winston, I do not understand. A MAX 5 amp fuse is less than the 6 amp MCB. The cable running to the device is protected by the MCB, the internal wiring? I have no idea. They specified 5 AMPs, not me.
     
  12. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,825
    Thanks Received:
    2,571
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Winston1 has been told several times that lighting circuits can be on a ring. He should not make statements which are not accurate for all installations.
     
    • Like Like x 1
  13. opps

    opps

    Joined:
    16 Jun 2006
    Messages:
    5,173
    Thanks Received:
    817
    Location:
    London
    Country:
    United Kingdom
    Perhaps, but in my case it was an error on my behalf.
     
  14. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,442
    Thanks Received:
    4,201
    Location:
    Retired to:
    Country:
    Portugal
    [​IMG]

    Those instructions are quite interesting and one for Winston's "wrong instructions" collection.

    They are clearly written and drawn by someone who just thinks that is what one should do with no regard to the regulations.

    Usually such instructions call for a 3A fuse and people argue that there might be something in the fan that requires 3A protection rather that 6A on the circuit. If there is - there isn't - then the manufacturer should fit a fuse in the fan - that's why they don't.
    Not to mention the horrible rest of the world fitting the same fans on 10A or 16A circuits with no fused switches being available.

    There is no argument that a 5A fuse has any advantage over a 6A MCB so stipulating one is just pointless.


    As to the positioning of the double-pole isolator before the light: this negates even the convenience of having an isolator so that, with a fault, the lights will still work - or the silly "You can work on the fan with the light on".
    The Wiring Regulations do not require local isolation for any appliance; not even the cooker or shower.


    So, were one to fit a three-pole isolator after the light, would one then be not complying with the manufacturer's instructions.
     
    • Like Like x 1
  15. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,182
    Thanks Received:
    158
    Location:
    Derry, Ireland
    Country:
    Ireland
    The cable does not need to be Earthed (and indeed most cable types can't be). A circuit protective conductor (cpc) must be run to and terminated at each point in the wiring (excluding some lampholders).
     
  16. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,442
    Thanks Received:
    4,201
    Location:
    Retired to:
    Country:
    Portugal
    Not sure I understand that.

    A conductor will only be a CPC if it is Earthed. Does that not count as 'Earthing the cable'?
     
    • Like Like x 1
  17. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,635
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    I think Risteard's ('pedantic') point was that, although a cable may contain an ('earthed') CPC (and must, per regs, contain one if it is the only cable going to 'the point' in the installation), it is generally not possible to 'earth a cable' - unless it has armour or some conductive covering/sheathing/whatever.

    Kind Regards, John
     
Loading...