Gas hob

Discussion in 'Plumbing and Central Heating' started by dormermike, 10 May 2021.

  1. dormermike

    dormermike

    Joined:
    1 Mar 2011
    Messages:
    744
    Thanks Received:
    14
    Location:
    Cardiff
    Country:
    United Kingdom
    Hello

    When my boiler kicks in, the lit burners on the hob all go down slightly until the boiler stops, and then return to normal. Just like the burner control knob is turned down slightly.

    Is this anything to be concerned at?

    For a bit of info, the boiler is next to the incoming gas main, and the hob is on the other side of the property on an approx 15m 15mm copper pipe run, T'd off from the boiler supply.

    Thanks
    DM.
     
  2. Sponsored Links
  3. Elkato531

    Elkato531

    Joined:
    22 Jul 2009
    Messages:
    1,085
    Thanks Received:
    277
    Location:
    Sussex
    Country:
    United Kingdom
    Gas supply issue possibly from undersized pipework. Could also be a faulty regulator on the gas meter. Get an RGI in to check working pressures at appliances and meter.
     
    • Thanks Thanks x 1
    • Like Like x 1
  4. Madrab

    Madrab

    Joined:
    4 Oct 2012
    Messages:
    8,036
    Thanks Received:
    2,274
    Location:
    East Renfrewshire
    Country:
    United Kingdom
    Yes ... you need to get a recommended GSR in to do a supply test ASAP. Chances are the pipe supplying both the hob and boiler isn't large enough and the boiler is drawing more than the pipe can deliver (unless there's a district pressure or meter/governor issue).

    Be prepared for the recommendation that a new gas pipe might need to be run.
     
    • Thanks Thanks x 1
    • Like Like x 1
  5. dormermike

    dormermike

    Joined:
    1 Mar 2011
    Messages:
    744
    Thanks Received:
    14
    Location:
    Cardiff
    Country:
    United Kingdom
    Thank you both, will take your advice.
     
    • Like Like x 2
    • Thanks Thanks x 1
  6. Sponsored Links
  7. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    14,635
    Thanks Received:
    3,202
    Location:
    Glasgow
    Country:
    United Kingdom
    Gold star to Dormermike to take given advice. There have been threads here for advice which then is rejected by the poster.
     
    • Like Like x 3
  8. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,555
    Thanks Received:
    2,244
    Location:
    North
    Country:
    United Kingdom
    And/or argued differently (y)
     
  9. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,740
    Thanks Received:
    1,086
    Country:
    United Kingdom
    Meter governor sticking. Mine has done it for about 5 years.
     
    • Thanks Thanks x 1
  10. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    12,259
    Thanks Received:
    3,250
    Location:
    Sussex
    Country:
    United Kingdom
    Why would you not get it replaced?
    It's obviously far more of a hazard on hobs not fitted with thermocouples where an unburnt gas incident could occur especially when the district pressure drops.
     