Heating on as per timer but pump shuts off after an hour ??

Discussion in 'Plumbing and Central Heating' started by curtly, 4 Nov 2013.

  1. curtly

    curtly

    Joined:
    6 Feb 2003
    Messages:
    36
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi guys, if somebody could offer any advice on my issue it'd be really appreciated.

    I've an old 'Glow-worm Fuelsaver' balanced flue boiler, with Drayton timer & stat. The timer correctly switches the heating on and radiators come on but only for around an hour then the pump goes off whilst the boiler is still correctly firing, after this I've noticed the pump comes on for brief periods of about 30secs or so then goes off again.
    The overall room temperature is still low so pump is not being switched off by the room stat.
    I've also double checked the room stat with a circuit tester and it correctly powers on and off when the dial is rotated.
    Tested the feed to the pump with the circuit tester and it confirms that the power to it is switching off after about an hour so the pump is fine.

    I'm guessing that it's either the controller or circuit board on the boiler unit, do the symptoms point to either of these or I have I missed something ?

    Thanks in advance for any advice

    Chris
     
  2. algas

    algas

    Joined:
    18 Oct 2008
    Messages:
    858
    Thanks Received:
    168
    Location:
    Devon
    Country:
    United Kingdom
    It could be the pump sticking when it gets hot.
     
  3. Sponsored Links
  4. curtly

    curtly

    Joined:
    6 Feb 2003
    Messages:
    36
    Thanks Received:
    0
    Country:
    United Kingdom
    Algas, did think that myself at first but i sat with a circuit tester on the feed next to the pump and it definitely powered off which stopped it, this is the only thing that's pointing me towards a 'control' issue :confused:

    Could a dodgy 3way valve cause the symptoms above ??
     
  5. jackthom

    jackthom

    Joined:
    14 Feb 2007
    Messages:
    1,365
    Thanks Received:
    242
    Location:
    Northumberland
    Country:
    United Kingdom
    The pump seems to be wired into the boiler thermostat on some of these models, presumably so that even when demand is removed it will overrun while the water temp is still high.

    I would take a look at the voltages around that temp control.
     
  6. Sponsored Links
  7. curtly

    curtly

    Joined:
    6 Feb 2003
    Messages:
    36
    Thanks Received:
    0
    Country:
    United Kingdom
    Bit more investigation tonight, opened up the 3-port motorised valve/actuator and the motor itself was red hot to touch, is this correct ?? Or have I found the problem ?
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page