Hot water venting cold water header tank

Discussion in 'Plumbing and Central Heating' started by ANGLER, 6 Mar 2018.

  1. ANGLER

    ANGLER

    Joined:
    7 Feb 2005
    Messages:
    172
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Increasing issues. Hot water from the emersion tank venting into the cold water tank, causing the water to level to reach the overflow.
    Hot water only used for kitchen and bathroom
     
  2. Sponsored Links
  3. Daveydub

    Daveydub

    Joined:
    18 Oct 2013
    Messages:
    1,722
    Thanks Received:
    589
    Location:
    Gloucestershire
    Country:
    United Kingdom
    Is your heating tank fed or sealed system?
     
  4. ANGLER

    ANGLER

    Joined:
    7 Feb 2005
    Messages:
    172
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    The tank is a indirect tank. The tanks are only used for kitchen and bathroom tap use.

    We have electric storage heating system.
     
  5. Daveydub

    Daveydub

    Joined:
    18 Oct 2013
    Messages:
    1,722
    Thanks Received:
    589
    Location:
    Gloucestershire
    Country:
    United Kingdom
    So nothing is connected to the coil in the cylinder?
     
    • Thanks Thanks x 1
  6. oldbuffer

    oldbuffer

    Joined:
    6 May 2010
    Messages:
    1,491
    Thanks Received:
    559
    Location:
    London
    Country:
    United Kingdom
    Assuming the hot water is heated only by the immersion heater (not by a boiler) then, if the hot water is extremely hot, the thermostat in the immersion heater may have failed, allowing the water to heat up too much. It then expands into the cold water storage cistern (CWSC), and will cause it to overflow.

    If it is this, then it needs fixing as a matter of urgency, or the CWSC could collapse and pour very hot water through the ceiling.
     
    • Thanks Thanks x 1
    • Like Like x 1
  7. ANGLER

    ANGLER

    Joined:
    7 Feb 2005
    Messages:
    172
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Last night I replaced the Immersion element & thermostat.
    Yet again warm water was being expelled out the overflow on the cold water header tank.
     
  8. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,331
    Thanks Received:
    1,326
    Country:
    United Kingdom
    There is a vent pipe that comes up and over the top of the tank ,and points down Into the tank ,is that where you have seen water coming from ? That's unlikely if you have just replaced the immersion element AND a new thermostat. Are you sure its not the float valve allowing water Into the tank when it shouldn't.?
     
  9. Daveydub

    Daveydub

    Joined:
    18 Oct 2013
    Messages:
    1,722
    Thanks Received:
    589
    Location:
    Gloucestershire
    Country:
    United Kingdom
     
  10. Sponsored Links
  11. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,331
    Thanks Received:
    1,326
    Country:
    United Kingdom
    Do you have a mixer valve ,shower or tap ,that is fed cold from the mains. Possible cross flow into gravity hot water system ?
     
    • Thanks Thanks x 1
  12. ANGLER

    ANGLER

    Joined:
    7 Feb 2005
    Messages:
    172
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Nothing connected to the coil
     
  13. ANGLER

    ANGLER

    Joined:
    7 Feb 2005
    Messages:
    172
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Haven't seen water at present emerging from the vent pipe, but the water being expelled outside is warm. Also contents of the cold water tank is also warm. Ball valve also replaced as a precaution.
     
  14. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,331
    Thanks Received:
    1,326
    Country:
    United Kingdom
    Mains cold water is getting into the dhw system if nothing is coming out the vent pipe.
     
  15. ANGLER

    ANGLER

    Joined:
    7 Feb 2005
    Messages:
    172
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    If this is happening, how can I prevent this?
     
  16. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,331
    Thanks Received:
    1,326
    Country:
    United Kingdom
    Establish where the cross flow is and eradicate . common on single handle lever taps, thermostatic mixer valves on showers ,bath fillers ,etc pumped hot to shower and mains cold to same. Its a process of elimination really.
     
    • Thanks Thanks x 1
  17. ANGLER

    ANGLER

    Joined:
    7 Feb 2005
    Messages:
    172
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Just let everyone know. The issue went away, when we upgraded our bathroom toilet. The previous toilet had an EYE wash attached, with a cold and hot water feed. The cross over must of occurred here.
    The toilet and upgrade was not done for this reason.
     
    • Like Like x 1