ideal response se will not fire up

Discussion in 'Plumbing and Central Heating' started by roymegs, 29 Apr 2011.

  1. roymegs

    roymegs

    Joined:
    29 Apr 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    Merseyside
    Country:
    United Kingdom
    Hi I have a ideal response se that often loses pressure whitch i can build up but if i dont it goes off and flashes 4-04 meaning non volatile lockout then i press reset it flashes 9-12 meaning flue stat cutout but will not restart. sometimes it will if left for a long time please help thank you roy
     
  2. Sponsored Links
  3. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    I dont know where you are getting your figures.

    The flue stat is intended to be non resettable!

    Many would say your boiler is working normally ( i.e. not working! )

    Tony
     
  4. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    As your faults seem to be associated with combustion/safety devices many would consider the best advice would be to get a registered engineer.

    Few understand these boilers very well and the diagnosis would aften be that you need a new boiler without having diagnosed exactly what the fault is. That should not be a chargeable statement!

    Tony
     
  5. bengasman

    bengasman

    Joined:
    28 Jan 2005
    Messages:
    34,181
    Thanks Received:
    3,124
    Location:
    London
    Country:
    United Kingdom
    Whatever the problem is, do not spend a lot of money on this boiler; they are complete lemons and it's a small miracle it has lasted this long.
     
  6. BDL

    BDL

    Joined:
    14 Oct 2003
    Messages:
    214
    Thanks Received:
    1
    Location:
    Kent
    Country:
    United Kingdom
    The Response se is a condensing Response. A Minimiser heat exchanger with a Honeywell/Grindfoss water set.

    Code 4-04 is just a generic lockout, the 2nd code that follows is the cause. 9-12 is the low water pressure switch. Concurrent with your comment the boiler loses pressure.

    Find out why it's losing pressure, leak somewhere? Look at the prv pipe outside?

    Job Done.
     
  7. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    In that case as the code represents a low pressure then you dont specifically need a gas registered engineer.

    But you do need to find out why its losing pressure and you may still need a competent heating engineer for that.

    Tony
     
  8. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    14,790
    Thanks Received:
    3,251
    Location:
    Glasgow
    Country:
    United Kingdom
    Also look under radiator valve caps to see if the valves are weeping
     
  9. roymegs

    roymegs

    Joined:
    29 Apr 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    Merseyside
    Country:
    United Kingdom
    Hi and thanks for your answers the leak appears to be coming from the saftey valve pipe that goes outside, and as for the water pressure switch i need to order one.once i replace that will the boiler then fire up as it wont at all now thanks again roy
     
  10. Sponsored Links
  11. MrGassafe2011

    MrGassafe2011

    Joined:
    28 Apr 2011
    Messages:
    20
    Thanks Received:
    0
    Location:
    Worcestershire
    Country:
    United Kingdom
    Also, Personally I would replace the schrader Valve core within the epansion vessel - this would be one cause of the PRV Leaking.

    If no further leaks are evident on the CHB/System
     
  12. roymegs

    roymegs

    Joined:
    29 Apr 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    Merseyside
    Country:
    United Kingdom
    Hi again, have replaced the water pressure switch on my ideal response se boiler and it still wont fire up.But on the water pressure switch it as 3 terminals with which 2 are used (1 and 3) number 2 as a plastic cover on. when i take the single red wire of 3 and put it on 2 it works fine and also there is no more leaks is this ok to swap them over your replys and answers would be much appreciated thanks roy
     
  13. mickyg

    mickyg

    Joined:
    24 Aug 2005
    Messages:
    16,007
    Thanks Received:
    3,325
    Location:
    Cornwall
    Country:
    United Kingdom
    its probably blocked behind the switch. Poke something in the hole. then put the terminals back where they were. Your basically linking out a safety device, very naughty mr.
     
  14. 45yearsagasman

    45yearsagasman

    Joined:
    14 Mar 2010
    Messages:
    6,094
    Thanks Received:
    1,093
    Location:
    Norfolk
    Country:
    United Kingdom
    No it is not ok to use the covered terminal. Investigate the reason why the new switch is not sensing pressure, ie there is a blockage or there IS no system pressure.
     
  15. roymegs

    roymegs

    Joined:
    29 Apr 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    Merseyside
    Country:
    United Kingdom
    Thanks for your replies,when i took the old switch off there was loads of brown gunk inside it could this be a problem,could the heat exchanger need cleaning thanks again roy
     
  16. adlplumbing

    adlplumbing

    Joined:
    9 Dec 2009
    Messages:
    6,341
    Thanks Received:
    998
    Location:
    Lancashire
    Country:
    United Kingdom
    get some out to check the main heat ex they prone to leaking if this is the case u need a new boiler :cry:
     
  17. roymegs

    roymegs

    Joined:
    29 Apr 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    Merseyside
    Country:
    United Kingdom
    HI, POKED SOMETHING IN THE HOLE BUT STILL SEEMS BLOCKED HOW DO YOU UNBLOCK THEM CHEERS ROY
     