Immersion heater, neutral wire keeps burning

Discussion in 'Electrics UK' started by limakilo0, 21 Apr 2010.

  1. limakilo0

    limakilo0

    Joined:
    21 Apr 2010
    Messages:
    3
    Thanks Received:
    0
    Location:
    Gloucestershire
    Country:
    United Kingdom
    Hello,

    I have had 3 different electricians in to look at my immersion heater (it's a manco combination cylinder) but none have come up with a solution.

    In July the water went luke-warm. Thermostat showed signes of burning. He replaced the element and thermostat. Since then, it heats the water properly but the neutral wire connection gets exceedingly hot within seconds of the immersion being switched on, which is why the neutral wire keeps burning off. Another electrician replaced the wire from the clock to the element but the neutral connection is still red-hot.

    Any answers please? It's not nice being relaint on a kettle!

    David
     
  2. Sponsored Links
  3. assured heating

    assured heating

    Joined:
    17 Sep 2007
    Messages:
    322
    Thanks Received:
    29
    Location:
    Essex
    Country:
    United Kingdom
    Its a loose conection to neutral try posting this in the electrical forum and you might get more respnse
     
  4. Boilerman2

    Boilerman2

    Joined:
    10 Jun 2009
    Messages:
    5,225
    Thanks Received:
    1,015
    Location:
    Suffolk
    Country:
    United Kingdom
    Try uprating the flex to 2.5mm/2 it is not un-common to find Immersion Heaters wired in 1.5mm/2 flex, which is getting near the mark for this size of cable, but nothing will cause a burnt neutral like a loose connection ;)
     
  5. TicklyT

    TicklyT

    Joined:
    30 Jul 2006
    Messages:
    3,481
    Thanks Received:
    337
    Location:
    Hampshire
    Country:
    United Kingdom
    You need mechanically sound connections between bright, clean metals at the terminals to carry the current.

    Any discolouration of the wire or terminal is probably an oxide layer formed when the connection first started overheating. Oxides have a high resistance, and cause further overheating and oxidation of the connection.

    Overheating also softens the copper in the cable, making it difficult to make a mechanically sound joint.

    Cut back or replace any heat damaged cable, and thoroughly clean the terminals before re-making the connections.
     
  6. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,817
    Thanks Received:
    1,962
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Rather than clamping the wire ends directly onto the element terminals, crimp a ring terminal on the end first:
    That way, the terminal can be tightened properly onto the flat surface of the ring, rather than the uneven multiple strands of the wire.
     
  7. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,990
    Thanks Received:
    1,354
    Location:
    Leeds
    Country:
    United Kingdom
    Can we have a photo please?
     
  8. ricicle

    ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,343
    Thanks Received:
    382
    Location:
    Gloucestershire
    Country:
    United Kingdom
    Any existing burnt wire needs to be got rid of back to clean, unaffected wire otherwise the problem will not go away. Also check that the connection is sound on the element post itself !
     
  9. limakilo0

    limakilo0

    Joined:
    21 Apr 2010
    Messages:
    3
    Thanks Received:
    0
    Location:
    Gloucestershire
    Country:
    United Kingdom
    Thanks for all your learned replies.

    I abandonned my original plan to do it myself and got another electrician in yesterday and he has put a temporary new cable (2.5mm) in between the immersion clock and the element. This appears to work as I can now keep my finger on the neutral terminal when it's on (before it was scorching hot within seconds). He didnt have any flexible cable so he's coming back on Saturday to finish the job off and also to replace the acble between "the feed" and the clock.
     
  10. Sponsored Links
  11. ricicle

    ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,343
    Thanks Received:
    382
    Location:
    Gloucestershire
    Country:
    United Kingdom
    Two things, make sure he does come back ASAP as normal t+e cable is not heat resistant and should not be used to connect up such an item (and is also not suitable for flexibility purposes either)

    Also it is not a good idea to put your finger on any terminal irrespective of it being Neutral, unless of course you are isolating first.
     
  12. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    36,919
    Thanks Received:
    1,272
    Country:
    United Kingdom
    Nucking Futter!

    So what's he wired it in instead? :eek:

    EDIT: sorry, rice, I didn't read what you put. :oops:
     
  13. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,685
    Thanks Received:
    278
    Country:
    United Kingdom
    I had a college lecturer whose favorite demonstartion was to stand on a wooden floor and touch the busbar tabs on a live DB :LOL:
     
  14. limakilo0

    limakilo0

    Joined:
    21 Apr 2010
    Messages:
    3
    Thanks Received:
    0
    Location:
    Gloucestershire
    Country:
    United Kingdom
    I was just following the example of my neighbour (who is a trained electrician, so he told me anyway!) not sure what you mean by "isolating first".

    I dont know what the temporary cable is. It's just grey coloured and quite rigid as it doesnt fold easily under the black cap that goes over the element and wiring.
     
  15. kai

    kai

    There is one neutral I can touch safely with the installation up and running - the combined neutral and earth terminal at the right hand side of the service fuse block (it sticks out of the side - to which the main earth is connected!) :LOL: :LOL: :LOL:
     
  16. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,990
    Thanks Received:
    1,354
    Location:
    Leeds
    Country:
    United Kingdom
    In theory at least ;)
     
  17. ricicle

    ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,343
    Thanks Received:
    382
    Location:
    Gloucestershire
    Country:
    United Kingdom
    As long as you haven't lost the network Neutral somewhere ;)
     