Hi Looked at an industrial unit today for testing theres a large open wharehouse unit with approx 60 fleurescents very high up.
Whats the way to test them without disconnecting all the lights.
dont get these very often thankfully.........
OS
depends on what type of flourescent if they are starter switch types then remove all the starters this will isolate Live from Neutral
No, just an IR test..... and see what the result finds
As a Periodic Inspection you mean? Is it possible to connect L&N together and IR test to earth?
Thats what I would do - although you may get shocking readings due to the inductors - they are never great.
They are designed for HT so 500v won't break them down to earth.
Yip thats what I was after, Question is would that test be ok and what readings am i likely to get. the fittings dont look as if they have been up long
should do test between L+N also.
ricicle said:
Not required if it is impractical to remove loads.Just L+N to E is suffice.
you can isolate L+N by removing all the starter switches if that type.
How do you remove the starters ;)
The regs call for the insulation resistance for a 500vDC test to be above 0.5 Meg, however anthing less than 2 Meg should be investigated further. Do you have a copy of guidance note 3?