It really doesn't does it? The 2.25mm is from the floor, not the bottom of the shower or bath.The below doesn’t sum that up great ...
That's not necessarily the case, in either direction. In one of my bathrooms, the bottom of the ('sunken') bath is about 500mm below the floor level!I suppose floor or bottom of bath shower is not going to be too much different.
Given that the OP has told us that the light would be 'over' the bath, the 600mm (horizontal) limits are irrelevant.Zone 2 is 600mm after that tho in each direction.
That's all wrong. Since the material you quoted was wrong, and the regs actually say that the zones stop at 2.25m above finished floor level, the light (at 2.6m above floor level) would not be in any zone. However, if it were less than 2.25m above floor level, since it is 'over' the bath, it would then be in Zone 1, not Zone 2.Which if you went from floor still means the posters light would be in zone 2.
Hmm care to share the source for why I am wrong please. It’s all good having an opinion but I actually checked many places to confirm my information. Can you do the decent thing and do the same and show please
From BS7671:2018 (the current version of 'The Wiring Regulations') ...Hmm care to share the source for why I am wrong please. It’s all good having an opinion but I actually checked many places to confirm my information. Can you do the decent thing and do the same and show please