Is 15mm Sufficient for Flow and Return

Joined
30 Dec 2009
Messages
30
Reaction score
0
Location
Bristol
Country
United Kingdom
Hi,

I'm in the process of having my house totally re-plumbed and with the exception of the first 1 -2 meters of pipe from the boiler, the plumber has used 15mm pipe for the entire flow and return.

The plumber tells me the size is irrelevant now the systems are pressurized.

Is this true or should it be 22mm?

The boiler is a Worcester 30i combi with 8 radiators.

Thank you in anticipation.
 
Sponsored Links
D

Doggit

The pressurisation has nothing to do with it; it's about carrying capacity on the flow and return. Someone will be able to do the calculations to prove it, but I just use a quick judgement, and with 8 rads, 22 is more sensible. Carrying capacity is why you have main roads, and side roads.
 
Sponsored Links
Joined
30 Dec 2009
Messages
30
Reaction score
0
Location
Bristol
Country
United Kingdom
The pressurisation has nothing to do with it; it's about carrying capacity on the flow and return. Someone will be able to do the calculations to prove it, but I just use a quick judgement, and with 8 rads, 22 is more sensible. Carrying capacity is why you have main roads, and side roads.

I suspect he's used 15mm pipe to increase his profit margins but now I have the difficult job of challenging him over a subject I know little about!
 
Joined
19 Nov 2007
Messages
3,088
Reaction score
612
Location
Lincolnshire
Country
United Kingdom
@fury84 As a quick rule of thumb and to keep it simple and calculation free for you to put to your plumber 15mm has a capacity of 4kw, 22mm has a capacity of 11kw and 28mm has 20kw.

If you only have 8 radiators and lets say each one is 1kw each you have a need for 8kw to pass through the system to allow for the correct temperature drop for the return to the boiler.

As you can see 15mm can only carry half of your required peak amount so you would need 22mm to ensure the correct capacity can be carried while your new boiler runs efficiently.

Like I said this is a very basic explanation and a general rule of thumb but should give you some helpful info to put to the plumber.

Jon
 
D

Doggit

If you check under the boiler, you'll find the flow and return pipes on the boiler are 22mm, not 15; so he should have continued in a likewise manner. You could try ringing Wosceter and see if the tech guys will talk to you. Have you paid him yet.
 
Joined
30 Dec 2009
Messages
30
Reaction score
0
Location
Bristol
Country
United Kingdom
Thanks guys.

The plumber is a accredited Worcestet installer!!! Might try calling them tomorrow.

Haven't paid yet.
 
Joined
19 Jun 2011
Messages
7,031
Reaction score
2,449
Location
Lancashire
Country
United Kingdom
the guy is a knob. Just shows that being an approved installer for the preferred choice of the installer doesnt guarantee a quality job.

more science involved than just throwing a white box on the wall. it will work until its paid for, then when the problems start, ring worcester then they will decline the warranty because it wasnt installed to MI's
 
Joined
30 Dec 2009
Messages
30
Reaction score
0
Location
Bristol
Country
United Kingdom
the guy is a knob. Just shows that being an approved installer for the preferred choice of the installer doesnt guarantee a quality job.

more science involved than just throwing a white box on the wall. it will work until its paid for, then when the problems start, ring worcester then they will decline the warranty because it wasnt installed to MI's

Going to ring them first thing tomorrow.
 
Joined
27 Oct 2007
Messages
819
Reaction score
223
Location
Essex
Country
United Kingdom
@fury84 As a quick rule of thumb and to keep it simple and calculation free for you to put to your plumber 15mm has a capacity of 4kw, 22mm has a capacity of 11kw and 28mm has 20kw.

If you only have 8 radiators and lets say each one is 1kw each you have a need for 8kw to pass through the system to allow for the correct temperature drop for the return to the boiler.

As you can see 15mm can only carry half of your required peak amount so you would need 22mm to ensure the correct capacity can be carried while your new boiler runs efficiently.

Like I said this is a very basic explanation and a general rule of thumb but should give you some helpful info to put to the plumber.

Jon

Absolute rubbish

8kw of rads with a DT of 20deg requires about 0.35 m3/hr in 15mm this will give a velocity of 0.55m/s and a head loss of approx 2.7m per 100m !!

please tell me why 15mm is incorrect if there is enough residual pump head in the boiler ?
 
Joined
20 Mar 2009
Messages
9,275
Reaction score
1,988
Location
Potters Bar
Country
United Kingdom
As said above... Call WB and ask their opinion, if they are happy to warranty it under that set up, that's all you need worry about and you can bury the hatchet with you plumber/heating engineer.
 
Joined
8 Dec 2007
Messages
14,396
Reaction score
5,690
Location
Cheshire
Country
United Kingdom
No more than 3 radiators on 15mm. It's not about how much heat it will carry in total, it's about making sure the radiators all work at the same time. Balancing 8 radiators on a 15mm would not be easy if not impossible. Put your calculators away and ask yourself would you do it.
 
Joined
20 Mar 2009
Messages
9,275
Reaction score
1,988
Location
Potters Bar
Country
United Kingdom
Personally, Jeff... I wouldn't do it!
If told to, by whoevers job it was, I do it then, but not be happy.
 