    I have a MEM consumer box. There is a 16 amp MEM breaker that supplies the immersion heater. I have had solar panels installed for the last two years and I have been having issues when I tried to install an Immersun device in place of the immersion heater timer switch, in that a fault develops. I am now onto my fourth unit. Suspecting (no particular reason) that it may be the old wiring from the consumer box I have replaced it just to rule that out. Whilst the end feeds are exposed before I fit the replacement, I thought I would check the resistance between the Live, Negative and Earth of the two respective cables (the one from the consumer unit and the one to the immersion heater. With the main isolating switch off, there is no measured resistance between the live, negative and earth cables of the feed, which is what I would expect. I am getting 19 ohms between the Live and negative for the immersion cable, which is also what I would expect. However, with the consumer box switched back on but with the immersion breaker off I am getting a measured resistance of about 17 M ohms between the Live and Negative of the feed from the box, about 18 M ohms between the Live and the Earth and about 1 to 2 ohms between the negative and the Earth. I am also getting a PD of about 8 volts AC across the Live and Negative. This seems very odd to me as surely there should be no measured resistance across any of the cables? I am not wanting to risk installing another unit as I am concerned that the consumer box may be at fault in some way. Any advice would be greatly appreciated.
     
    • Thanks Thanks x 1
  2. Sponsored Links
  3. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,565
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    If you are getting that, then there is a fault either with the wiring, or the immersion element. The resistance between earth and the line or the neutral should be more than 2,000,000Ω (2MΩ)

    It should be reasonably easy to track down, As you have a meter, and an identified fault.
     
  4. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,202
    Thanks Received:
    557
    Location:
    London
    Country:
    United Kingdom
    There is no negative on AC, is is called neutral.

    One or two ohms between neutral and earth once the main breaker is on is not necessarily a fault. If, say, your are on a PME system the neutral and earth will be connected together where it comes into the house. I'm surprised TW does not realise this.
     
    • Thanks Thanks x 1
  5. jimbo5050

    jimbo5050

    Joined:
    12 Oct 2004
    Messages:
    66
    Thanks Received:
    2
    Location:
    Aberdeenshire
    Country:
    United Kingdom
    Thank you for the replies. That sounds like everything is okay then, so I will go ahead and fit the unit and keep my fingers crossed.
     
  6. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    [​IMG]
     
  7. Sponsored Links
  8. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,175
    Thanks Received:
    1,279
    Country:
    United Kingdom
    I like that bas, wish I knew how you did it. regards terry
     
  9. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,565
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Mea Culpa. I didn't read the post properly. :oops:
    Thought he was testing towards the immersion. Must be the heat…
    Of course, as Winston says, you will see a low impedance between neutral and earth.
     
  10. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Find an image on the interwebby that you want to post, and copy the URL.

    In your post, click the image button [​IMG] and insert the URL.
     
  11. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,183
    Thanks Received:
    158
    Location:
    Derry, Ireland
    Country:
    Ireland
    It is also called phase 50% of the time.
     
  12. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,937
    Thanks Received:
    1,991
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    If measured with a typical multimeter, that is due to capacitive coupling between the immersion cable and other adjacent cables.
    It's also probably why the 17Mohms appears, as even a tiny voltage on the cable will cause defective readings - multimeters typically apply a couple of volts to the cable when testing for resistance, so any voltage from other sources will give totally misleading results.
     
  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page