i have a logic ideal combi. problem is when i have the heating on the boiler will run for a few minutes, then cut out. after a few more minutes it comes back on. and then cuts out . it will do this all the time. the rads at best are only luke warm.the pressure is ok. i have also bled all the rads. hot water is ok. hot water is ok. thanks for any help, advice.
 
Sponsored Links
Sponsored Links
Joined
17 Aug 2009
Messages
40
Reaction score
0
Location
Carmarthenshire
Country
United Kingdom
looks clean. If I need to flush the system what would be the best methods. It is a microphone 10ml. If I open the drain tap at the lowest point, then open the fill tap on boiler, do you think this would work. Thanks for reply.
 
Joined
30 Dec 2018
Messages
10,757
Reaction score
1,454
Country
United Kingdom
If it's clean - no need to flush it.

Yes you could run a pipe from a drain tap and just open the fill point, making sure you don't over pressurise the system, then see what flushes out. Better is taking individual radiators outside and forward/back flushing them out. You can get solutions to leave in your system to help clean it out, combined with flushing.

You can run a magnet along copper pipes you suspect might be obstructed - magnet will be pulled to the pipe, if it is blocked with magnetite/rust.
 