Nest install sanity check

Joined
10 Jun 2012
Messages
75
Reaction score
1
Location
Shropshire
Country
United Kingdom
Hiya,

We have a Logic 35 combi boiler in the airing cupboard in our bedroom. The thermostat is a honeywell 907 battery operated stat downstairs in the hallway connected by wiring in the wall. It only has two wires connected to it to control the call for heat.

Looking to delete/remove the honeywell by disconnecting at the boiler and covering with a blanking plate at the wall then install the heatlink for the nest near the boiler via a run in trunking of maybe 1.5 metres.

My plan is to use 5 core heat resistant flex to carry the 230v l/n supply directly from the boiler's internal terminal block (is off a 3amp fused spur) to the l/n on the nest and then the two call for heat cables to terminal 1-3 on the nest.

Two questions:
  • Is 5 core (4 core and earth) 0.75mm heat resistant flex okay for this application? (https://www.toolstation.com/shop/p14950)
  • Is this notifiable work, and thus would I be better off getting a trained professional to fit? (I've replaced lights, led drivers, basic soldering etc. so I'd like to think competent enough to install 4 wires)

Boiler diagram:

luXdICr.jpg
 
Last edited:
Joined
15 Aug 2010
Messages
24,959
Reaction score
11,156
Location
Livingston
Country
United Kingdom
yes 5 core 0.75 mm is the correct cable to use and no it is not notifiable, but access to the wiring means removing the combustion cover, which you really should be registered to do this
 
Sponsored Links
Sponsored Links
Joined
10 Jun 2012
Messages
75
Reaction score
1
Location
Shropshire
Country
United Kingdom
Ok will give my trusted plumber/heating engineer a call. Seems a bit strange to call a heating guy for a wiring job but I get it not worth risking anything especially as it's in the bedroom
 