    Hi guys
    I have a reavenheat boiler
    Today I drained part of the system to replace a towel rail,
    After completing the job I refilled the system using the loop under the boiler ,unfortunately the gauge remains to zero
    I have bled the rads and refilled the system but the gauge is still on zero
    I fired up the boiler and everything works fine , hot water and heating
    Even with the rads hot the pressure is still zero!!!i have switched everything off for the night to avoid damage
    Can anyone help??????
     
  2. Sponsored Links
  3. echoes

    echoes

    Joined:
    27 Mar 2007
    Messages:
    1,246
    Thanks Received:
    142
    Location:
    Surrey
    Country:
    United Kingdom
    Either:

    1) The gauge is faulty or has become blocked. What was it reading before the work?

    2) You have not pressurised the system enough. Does water squirt out if you bleed the highest radiator?
     
  4. Broddoy

    Broddoy

    Joined:
    24 Jan 2012
    Messages:
    3
    Thanks Received:
    0
    Location:
    Sussex
    Country:
    United Kingdom
    Before. I started the work on the rads pressure was just 1 bar
    But it never went over 1 bar possibly due to the fact that the boiler is in the loft
    And in answer to your question I have filled a cup of water from each rad
    Reading on other forums I have heard of a fault in some membrane and water mixing with air ???
     
  5. Mr Smyth

    Mr Smyth

    Joined:
    26 Nov 2005
    Messages:
    277
    Thanks Received:
    25
    Location:
    Surrey
    Country:
    United Kingdom
    Either the gauge is faulty or simply blocked, probably blocked.

    Kill the power and confirm its killed, drain the appliance, trace the thick wire that comes out of the back of the gauge and remove the other end probably from the return manifold. Poke through the muck that has accumulated in the connection and clean the wire end. Be careful with the o-ring but maybe a compression connection. Refill the system and test.

    Go for the unblocking first as that will tell you whether the gauge is faulty.

    Hope this helps
     
  6. Broddoy

    Broddoy

    Joined:
    24 Jan 2012
    Messages:
    3
    Thanks Received:
    0
    Location:
    Sussex
    Country:
    United Kingdom
    Thanks mr smith
    Are you familiar with this reavenheat boiler ?
    Is there a quick way to empty it ?? Or do I need to undo one of the pipes??
    I was wandering if I could use the drain pressure valve located at the bottom of the boiler
     
  7. Mr Smyth

    Mr Smyth

    Joined:
    26 Nov 2005
    Messages:
    277
    Thanks Received:
    25
    Location:
    Surrey
    Country:
    United Kingdom
    I would go for the same way you drained it before. Just releasing the pressure is normally enough.

    Not sure if this boiler has a drain point. Opening the PRV is not a good idea as it can lead to other problems.
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page