periodic codes
25 Feb 2010
Lancashire
hi all,
im just wanting to know a thew codes that im unsure of
on a ringmain circuit there is no end to end on earth to earth and n-n
poor IR readings on sockets as low as 20-60 M ohm
and no heat sleving on bathroom light
thanks
• Code 1 Requires urgent attention
• Code 2 Requires improvement
• Code 3 Requires further investigation
• Code 4 Does not comply with BS 7671
hi all,
I'd say a 2 if only 1 break in CPC (so long as measured Zs is OK) or a 1 if more than 1 break
20M-60M ohms is perfectly acceptable - no code
If it's suffering from heat damage then code 2 otherwise I wouldn't code it
thanks
Mine in bold
Have a look at the ESC guidance, loads of good info in it!
What are the concequences of the ring final being open circuit on CPC and neutral??
What is wrong with 20 meg insulation resistance reading??
Does the bathroom light need heat sleeving??
higher fault loop impedances
Potential for overloading cables depending on how the ring is loaded and where the break is.
Depending on how the break occoured the break itself could a further hazard such as a damaged cable or wires loose in a socket that could fal out or short at any time.
In reality that shouldn't be a problem as a spur only has a single piece of 1.5mm cpc