Probably a bit of a repeated question.... BUT....
I am in the process of paving my entire back garden at the request of SWMBO. She is also asking for a single and a double socket to be installed in the garden. Obviously these will need to be IP56 rated etc.
The patio is not yet laid, so I am open to possibly digging the cable in but want to explore what may options are.
The nearest power is on a RCD protected (at the CU in the house) mains ring that supplies only the kitchen (this ring is separate from the CU supply to the cooker and fridge/freezer
.
1) Can I run a fused spur from this mains ring outside to the first socket (single socket about 5 metres away), and then run the cable straight on to the second socket (double socket) about a further 10 metres away?
2) Is it absolutely neccessary to bury the cables, or can I just use PVC conduit running along boundary walls with T&E inside (is that allowed??). What options are there? I can still bury the cables as the patio is not yet laid, but conduit might be preferred as it will be far easier to move things later if required.
3) What size cable would I need. The only things that would be plugged into the sockets would be:
* 1500W pressure washer
* Occassional power tools, nothing heavy... circular saw/router up to 1Kw
* external lighting, no more than 500w maximum (filament/low energy mains type, not halogen or LV).
At the moment I am thinking that burying the cable is probably best (at least 450mm deep, I recall others saying?). Can I just use SWA and bury it at the correct depth, properly marked/protected etc?
Does SWA that is above ground need to be run in conduit? So if the SWA came out through a wall, and down the wall into the ground would it need any protection?
Part P disclaimer..... My BIL is a qualified sparky and inspects all my work prior to it getting turned on, so no danger of it being a train wreck. He just prefers that I don't bother him until I need something inspecting/signing off/certifying (or whatever it is that needs doing)... which suits me fine as he is a bit of an ar5e. So no part P references please.
[/list][/list]
I am in the process of paving my entire back garden at the request of SWMBO. She is also asking for a single and a double socket to be installed in the garden. Obviously these will need to be IP56 rated etc.
The patio is not yet laid, so I am open to possibly digging the cable in but want to explore what may options are.
The nearest power is on a RCD protected (at the CU in the house) mains ring that supplies only the kitchen (this ring is separate from the CU supply to the cooker and fridge/freezer
1) Can I run a fused spur from this mains ring outside to the first socket (single socket about 5 metres away), and then run the cable straight on to the second socket (double socket) about a further 10 metres away?
2) Is it absolutely neccessary to bury the cables, or can I just use PVC conduit running along boundary walls with T&E inside (is that allowed??). What options are there? I can still bury the cables as the patio is not yet laid, but conduit might be preferred as it will be far easier to move things later if required.
3) What size cable would I need. The only things that would be plugged into the sockets would be:
* 1500W pressure washer
* Occassional power tools, nothing heavy... circular saw/router up to 1Kw
* external lighting, no more than 500w maximum (filament/low energy mains type, not halogen or LV).
At the moment I am thinking that burying the cable is probably best (at least 450mm deep, I recall others saying?). Can I just use SWA and bury it at the correct depth, properly marked/protected etc?
Does SWA that is above ground need to be run in conduit? So if the SWA came out through a wall, and down the wall into the ground would it need any protection?
Part P disclaimer..... My BIL is a qualified sparky and inspects all my work prior to it getting turned on, so no danger of it being a train wreck. He just prefers that I don't bother him until I need something inspecting/signing off/certifying (or whatever it is that needs doing)... which suits me fine as he is a bit of an ar5e. So no part P references please.