Radiator woes

Sponsored Links
Joined
18 Jul 2014
Messages
35
Reaction score
2
Location
Gwent
Country
United Kingdom
Sorry when I say virtually closed I mean it's just cracked a tiny bit so a 1/16 of a turn maybe and that's on all of them bar the kitchen and they are all still hot. Flow on kitchen rads now to up high 50s with return being 12 to 15 degrees lower. Doesn't seem excessively cooler but don't think I can close other lockshields any further without shutting off the radiators. Maybe I can sneak the towel radiators a little more as they seem to have a massive impact on the whole system even being only a tiny bit open on the flow and return.
 
Joined
18 Jul 2014
Messages
35
Reaction score
2
Location
Gwent
Country
United Kingdom
Hi all, bit of an update, while poking around in the cupboard with the cylinder and valves I noticed a gate type bypass valve above the cylinder return pipe and before the 2 port motorised valves which was fully open. In other words a large proportion of flow from the boiler would have been going through the pump and then straight back to the boiler as the path of least resistance while only some would have gone through the motorised valve to the rads. I've shut this now bar the last 1/4 turn and my rads have never been hotter, they are hotter now than the fires of hell. I suppose I have some more balancing to do!
 
Sponsored Links

DP

Joined
10 Dec 2003
Messages
15,648
Reaction score
3,535
Location
Glasgow
Country
United Kingdom
Try running the system with hot water zone switched off ( if you have that option)
Not unsusual short 22 mm run into cylinder coil can do cause issues with radiator circulation

:notworthy::notworthy: Wrote above and then read the clear :rolleyes::rolleyes::rolleyes:
 
Joined
18 Jul 2014
Messages
35
Reaction score
2
Location
Gwent
Country
United Kingdom
My only concern now is that is this bypass valve supposed to be closed or partially cracked? I'd hate to solve one issue only for it to be doing longer term damage to the boiler
 
Last edited:
Joined
18 Jul 2014
Messages
35
Reaction score
2
Location
Gwent
Country
United Kingdom
Ok so pump most definitely does not like that valve being closed. Must be required for pump overrun. Have closed it 3/4 a turn now, looks like I'll have to play tunes on this Vs balancing radiators. I knew it was too easy!
 