Raveheat boiler losing pressure

Discussion in 'Plumbing and Central Heating' started by female222, 5 Feb 2012.

  1. female222

    female222

    Joined:
    5 Feb 2012
    Messages:
    2
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Hi, I have a Ravenheat 820/20T boiler. The central heating stat on the boiler is turned down to almost lowest point. The heating is only on for 10/15mins and water comes out of the pipe that goes outside. The water pressure goes up to about 2.5 bar so not at the max 3 bar. Can anyone help please? Many thanks
     
  2. Sponsored Links
  3. weareleeds

    weareleeds

    Joined:
    13 Dec 2005
    Messages:
    664
    Thanks Received:
    2
    Location:
    Yorkshire
    Country:
    United Kingdom
    expansion vessel flat or pipe blocked
     
    • Thanks Thanks x 1
  4. female222

    female222

    Joined:
    5 Feb 2012
    Messages:
    2
    Thanks Received:
    0
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Thanks for your reply, just had boiler man out and he says the vessel needs repressurising. Thanks for your help again at least i know i'm not being ripped off.
     