Regs and kitchen electrics

Joined
4 Jan 2004
Messages
390
Reaction score
2
Location
Devon
Country
United Kingdom
Assuming the definition of "kitchen electrics" to include:
- fused spur for under-unit lighting
- ring sockets for dish washer, washing machine, fridge, kettle, etc.
- separate 30A circuit for cooker/hob
Then current IEE regulations do not require these circuits to be retrospectively fitted with RCD protection in the event that a kitchen be modernised in an older property with a fused (i.e. non-mcb protected) consumer unit.

True or false?

If false, please quote IEE regulation which requires RCDs to protect these circuits.
 
Sponsored Links
yes they ring should have a RCD. any socket where an extension could be plugged in and taken outside should have a RCD
 
But if kitchen is 2 stories up......? No chance of external plugging in, therefore not applicable. Correct?
 
Sponsored Links
If the incomming supply is TT type then the whole installation should be protected by RCD.
REG 413-02-19
If not a TT system then I can't find a reg that states the kitchen circuits are to be rcd protected.
 
well it says all sockets that can feasiblly supply equipment outside the equipotential zone should be on a 30ma rcd in any installatino type

this is often interpreted to mean all downstairs sockets but there is some disagreement over this

and kitchens are usually downstairs
 
My Kitchen is on the Top floor of a Four Storey block of flats - hence the No Need for an RCD as per regulations - but it doesn't stop one being provided! :LOL: :LOL: :LOL:
 