Hi
I currently have a mechanical Honeywell T4160 Thermostat and would like to replace the unit with a digital thermostat a REV100.
The current unit is wired as:-
2 - Single Black (Separate cable)
3 - one of a pair of red
1 - second of the pair of red
Earth not used. I believe this circuit switches the motorised valve in an S plan system. The motorised valve in turn switch the pump and boiler.
If I check the circuit with a meter I get the following
Stat below temp
1 & 3 = 240V
1 & 2 = 0V
Stat above temp (I.e turn heating on)
1 & 3 = 0V
1 & 2 = 240V
2 & 3 always read 240V
Now on my new Digital Siemens REV100, I only have two connectors, L and L1 (T1 & T2 for remote sensor only I think).
Does anyone know how to swap over the connections.
I tried Single Black to 2nd of red pair, but this popped the circuit breaker.
Thanks in advance.
I currently have a mechanical Honeywell T4160 Thermostat and would like to replace the unit with a digital thermostat a REV100.
The current unit is wired as:-
2 - Single Black (Separate cable)
3 - one of a pair of red
1 - second of the pair of red
Earth not used. I believe this circuit switches the motorised valve in an S plan system. The motorised valve in turn switch the pump and boiler.
If I check the circuit with a meter I get the following
Stat below temp
1 & 3 = 240V
1 & 2 = 0V
Stat above temp (I.e turn heating on)
1 & 3 = 0V
1 & 2 = 240V
2 & 3 always read 240V
Now on my new Digital Siemens REV100, I only have two connectors, L and L1 (T1 & T2 for remote sensor only I think).
Does anyone know how to swap over the connections.
I tried Single Black to 2nd of red pair, but this popped the circuit breaker.
Thanks in advance.