Replacing a Salus iT500 RX with3rd Gen NEST and Worcester 30CDi conventional boiler

Discussion in 'Plumbing and Central Heating' started by MatCapri, 11 May 2020.

  1. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    Hello, my Salus wi-fi Gateway has finally died and it's time to replace the unreliable system with a Nest.

    Could anyone advise on wiring the Nest heatlink to replace the iT500 RX receiver unit please?

    The current wiring is as per the images attached, as follows:

    1. Red cable from CH COM to CH L
    2. Red cable from CH COM to AUX COM
    3. Yellow cable from wall to CH NO
    4. Brown cable from wall to CH L
    5. Red cable from wall to CH L
    6. Grey cable from wall to N
    7. Black cable from wall to N
    8. Red cable from wall AUX NO

    And then there are terminated black and blue cables and a separate terminated earth. I assume these can remain or the earth can be connected to the heatlink earth.

    Am I correct in the following for the heatlink:

    1. Red cable from (2) to L
    2. Red cable from (2) to (5)
    3. Yellow cable from wall to (3)
    4. Brown cable from wall to L
    5. Red cable from wall to L
    6. Grey cable from wall to N
    7. Black cable from wall to N
    8. Red cable from wall to (6)
    9. Earth to earth

    Any help would be greatly appreciated.

    Thanks.
     
  2. Sponsored Links
  3. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    7,915
    Thanks Received:
    2,041
    Location:
    North
    Country:
    United Kingdom
    Hi Mat,

    No images are available to view.
     
    • Thanks Thanks x 1
  4. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    22,315
    Thanks Received:
    8,837
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Colours of wires mean absolutely nothing on heating wiring
     
  5. picasso

    picasso

    Joined:
    8 Apr 2008
    Messages:
    10,562
    Thanks Received:
    2,640
    Location:
    Essex
    Country:
    United Kingdom
    3.jpg 4.jpg

    From his media page.
     
    • Thanks Thanks x 2
  6. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks both, I thought I'd attached them, appreciate your input.
     
  7. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    If it helps at all, this is the layout of the control unit's connections - the labels are obscured by the cables on the actual device so thought this might be useful. Cheers.
     

    Attached Files:

    Last edited: 12 May 2020
  8. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
  9. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    :)
     
    Last edited: 13 May 2020
  10. Sponsored Links
  11. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,591
    Thanks Received:
    1,524
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    By Conventional Boiler, I assume you mean one connected to central heating and a stored hot water system (ie hot water cylinder). If so, the wires simply move from the Salus terminals, to the Nest Heat link terminals that have exactly the same function.

    So, the wires in:

    IT 500 RX CH C = Nest Heating: Common

    IT 500 RX CH NO = Nest Heating: Call for Heat

    IT 500 RX L = Nest L

    IT 500 RX N = Nest N

    IT 500 RX Aux NO = Nest Hot Water: Call for Heat

    IT 500 RX Aux C = Nest Hot Water: Common

    If you want to use the Heat link to power the Nest Thermostat instead of using a separate plug in power supply, additional wires will need to be run from Heat link T1 & T2 to the Nest thermostat T1 & T2. If this is done, the Heat link also needs an earth connection making to the earth terminal just to the left of T1.
     
    • Thanks Thanks x 2
  12. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks @stem appreciate your help.

    Yes, that's what I meant by conventional - I was trying to differentiate from a combi boiler which ours it not. Thanks for clarifying that, it's an 'S' plan system with the boiler connected to the CH and HW cylinder.

    That makes sense then re: the connections, thanks for confirming. Can I just ask, with reference to the 'jumper' cables, i.e those wires running between the iT500 connections, not coming from the wall:

    1. Jumper cable from CH COM to CH L
    2. Jumper cable from CH COM to AUX COM

    Am I correct in thinking these need to remain in place on the heatlink as follows:

    1. Jumper cable from Nest Heating: Common to Nest L
    2. Jumper cable from Nest Heating: Common to Nest Hot Water: Common

    I think I'll use a separate plug-in power supply for the Nest Thermostat, I've got suitable place where it can be fixed and where a power supply can be pulled through from the wall behind.

    Thanks again,

    Mat.
     
  13. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,591
    Thanks Received:
    1,524
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Hi Mat
    Yes, all wires should remain connected as they are including the jumpers.

    The order of the 'jumpers' can be different if it's easier. Provided that the Heat link (L) is also connected to the commons (2) and (5), you can then introduce the actual 'live' supply wire to any of the three as they are all joined together it doesn't matter which.
     
    • Thanks Thanks x 2
  14. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    You're a gent @stem thank you. I'll let you know how I go. Cheers.
     
    • Like Like x 2
  15. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    IMG_0111.jpeg IMG_0112.jpeg

    Looking good @stem thanks again - now just to tidy up the walls...

    Cheers,

    Mat
     
    • Thanks Thanks x 1
    • Like Like x 1
  16. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    7,915
    Thanks Received:
    2,041
    Location:
    North
    Country:
    United Kingdom
    Well done Mat. (y)
     
    • Thanks Thanks x 1
    • Like Like x 1
  17. MatCapri

    MatCapri

    Joined:
    11 May 2020
    Messages:
    9
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks @Chris_W, just had to reset to get it to recognise hot water on/off but seems to be working fine now. Cheers.
     
    • Like Like x 1
  18. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page