Residential 3 Phase Supply to Single / 3 Phase

Discussion in 'Electrics UK' started by sparkypenguin, 18 Sep 2021.

Tags:
  1. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,603
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    As you say, it certainly is not necessary, and I would be very surprised if (m)any people over-sleeved the brown of single-phase circuits with black or grey, even if all three phases were present in the installation as a whole.

    However, whilst you say that the over-sleeving "could be done" (which, literally, is obviously true!), I wonder whether, strictly speaking, it would be compliant with BS7671, given that Table 51 indicates only brown as the colour which should be used to identify a line conductor in a single-phase AC circuit?

    Kind Regards, John
     
  2. Sponsored Links
  3. TimboTwo

    TimboTwo

    Joined:
    30 Jan 2021
    Messages:
    156
    Thanks Received:
    28
    Country:
    United Kingdom
    Why don't you ask your electrician about this?
     
  4. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,603
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    I agree with more-or-less everything that has been said to you about your proposed 3-phase board.

    However, although it's presumably far too late for me to be asking, I can't help but wonder whether you actually need/needed a 3-phase supply. Do you actually have, or envisage that you will have, any 3-phase loads (you hint that you might be considering 3-phase EV charging, but nothing beyond that?).

    Although, just to confuse things, my house is 'an exception which proves the rule' :)-) ), the vast majority of domestic properties in the UK (including those which have, or will have, EV charging) have single phase supplies - and the only usual reasons for wanting a 3-phase supply would be if one had loads which required such a supply, or if the total demand was too great for a standard (usually 100A maximum) single-phase supply (which would be unusual for a "2.5 floor" property).

    For what it's worth, my large house ("4+ storey" - 3 floors + full-size cellar + attic) has (but doesn't really need!) a 3-phase supply and I've arranged that in one of the ways suggested above - with multiple single-phase CUs/DBs scattered around the house, spread over the phases on roughly a 'one per floor' basis, which offers some advantages. If I had, or ever come to have, any equipment which requires a 3-phase supply, it would be very simple to add a small further, 3-phase, DB to service the required circuit(s).

    Kind Regards, John
     
  5. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,603
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Indeed. Given the number and nature of the questions he's asked here, he is clearly going to have to do that.

    Kind Regards, John
     
  6. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,138
    Thanks Received:
    550
    Location:
    London
    Country:
    United Kingdom
    OK. Makes sense.
     
  7. sparkypenguin

    sparkypenguin

    Joined:
    11 Jan 2009
    Messages:
    64
    Thanks Received:
    2
    Location:
    Tyne and Wear
    Country:
    United Kingdom
    Thanks very much for all the input (y), I'll try and respond to all questions in a logical order....


    I will but I always like to have multiple opinions about any aspect of my build and to learn about what's possible etc, after all it's very rare that there is only one solution and it does allow me to have a more meaningful conversation!


    Reasons for going 3 phase..
    I personally don't believe that 18KW is enough for a modern new build given that more stuff is going to go electrical, and although I do have a gas supply to the property, I am not planning to install any gas components.
    I may wish to install a 22KW EV, my solar panels are potentially going to be a 10KW 3 phase system, my air source heat pump is potentially going to be a 3 phase model, I will also have an electric oven / hob and 1 electric shower. Plus it did not cost much more to go 3 phase so I could not see any downside.
    As for splitting the supply to single phase DB's over the floors this is not something I even considered. I did start off planning to use separate DB's but just assumed they all had to be close to the meter and therefore all in the garage and 90% of the top floors cabling is already in place. Plus I only just found out yesterday morning that I could use a 3 phase DB and simply take single phases from it and hence I am thinking I may as well use a 3 phase board to give more flexibility going forward.


    I thought that a standard board was what I needed?
    I understand about the number of ways so 12 way or maybe slightly larger.
    I'll look for a board with incomer and thanks for promoting me to "rookie" level :).
    I only just started looking into the design of the system yesterday morning and not planning to order the board yet, I just wanted to get an idea of what was possible / allowed etc so I can discuss with my electrician and also to allow me to consider any implications on other aspects of the build.


    This is a copy of my last post and I have received 2 responses.....
    and
    They appear to contradict each other as one assumes only the neutral will be shut off and the other states that the entire supply will be shut off?
    And if anyone can shed any light onto whether my 3 phases need to be balanced and whether 18KW on one phase whilst zero on the other 2 could potentially cause a dangerous neutral current.
    And although it may not be "needed" for an average install I would rather fit some form of protection if the only downside is the extra cost?


    As I have stated I only have a basic knowledge of electrics and I did only start to look into this yesterday morning. I have taken a photo of the incoming supply which may help?
    20210918_171405.jpg
    20210918_171409.jpg
    20210918_171412.jpg

    Thanks again for all the continued help (y)(y)
     

    Attached Files:

  8. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,182
    Thanks Received:
    158
    Location:
    Derry, Ireland
    Country:
    Ireland
    The EVSE will need to be wired through a 4 pole RCCB, as it must interrupt all live conductors.
     
    • Thanks Thanks x 1
  9. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,182
    Thanks Received:
    158
    Location:
    Derry, Ireland
    Country:
    Ireland
    They shouldn't be sleeved, as single phase circuits are required to be identified by brown for the phase (line).
     
    • Thanks Thanks x 1
  10. Sponsored Links
  11. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,908
    Thanks Received:
    1,985
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    18kW is approximately 78 amps.

    With 78 amps on one phase and nothing on the other two, the neutral current is 78 amps.
    With all 3 phases at 78 amps, the neutral current is zero.
    The only circumstances where the neutral current can exceed that of one phase is where harmonics are present. The solution there is to remove the harmonics, not install spurious overload devices.
    You don't need neutral overcurrent protection.

    Phases should be balanced, and by installing a standard 3 phase board they will be. However nothing will happen if they are not balanced, or if for some reason al the loads in use at a particular time were on one phase.

    Surprising that they actually installed a 3 phase cutout in a small SP meter box.
    Hopefully it will be small meter.
     
    • Thanks Thanks x 1
  12. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,698
    Thanks Received:
    280
    Country:
    United Kingdom
    It is IMHO, I was just a little unsure why the modified picture was shown as if to illustrate something that you thought was unusual :)

    You mis-understand generally all commercial boards come without incommer, you order the incommer you need as a separate item, as opposed most domestic boards where the incommer is supplied as standard, thats why its a rookie mistake to forgot to add the incommer, it was a half tongue in cheek comment when you copied the description of a board without incommer as asked "Is this what I need?" :) It certainly wouldn't be the first time I've seen someone who does mostly domestic work have to take a second trip back to the wholesaler!
     
    • Like Like x 2
    • Thanks Thanks x 1
  13. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,523
    Thanks Received:
    421
    Location:
    Kent
    Country:
    United Kingdom
    It's OK to ignore winstons reply as he doesn't know what he's talking about as demonstrated in his reply to Rockys correct post
     
    • Like Like x 1
  14. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,138
    Thanks Received:
    550
    Location:
    London
    Country:
    United Kingdom
    It is very rude to tell people to ignore other members replies. Especially when I DO know what I am talking about. FACT if the neutral is disconnected the phase voltage could rise to 415 volts. Rocky’s explanation of course was also correct.
     
    • Like Like x 1
  15. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,182
    Thanks Received:
    158
    Location:
    Derry, Ireland
    Country:
    Ireland
    The harmonised voltage is 400V.
     
  16. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,523
    Thanks Received:
    421
    Location:
    Kent
    Country:
    United Kingdom
    It's also very rude to post uninformative and, in this case, incorrect advice. OP even pointed out there was contradiction between the two posts and then you verified your error by posting
    As to your latest... FACT... (yes I can shout too)...
    Hmmm I'd rather expect phase voltage to be a nominal 400V all the time and 415V is well within the current standards. What is your point?
     
    Last edited: 19 Sep 2021
  17. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    8,417
    Thanks Received:
    902
    Location:
    Essex
    Country:
    United Kingdom
    Neutral monitoring i recall is more used when the Neutral conductor size is reduced compared with the phase conductors, i would guess its more used in Network distribution supplies.
    you are correct to say it would be foolish too somehow break just the Neutral conductor.
     