Discussion in 'Plumbing and Central Heating' started by postflop, 3 Sep 2021.

  1. postflop

    postflop

    Joined:
    22 Dec 2009
    Messages:
    37
    Thanks Received:
    0
    Location:
    Belfast
    Country:
    United Kingdom
    Hi
    I am having a problem with resistance in the motor shaft of a riello 40 burner which is causing the burner to lock out and not restart after running for 30 minutes or so. I have replaced the oil pump and the motor bearings but the problem is still there. There is also a medium level warbling noise when the burner is running which is definitely coming from the motor area but doesn't seem to be the bearings.
    The fan seems to move freely when the pump is detached so I'm guessing the oil pump is causing the problem. Although, as mentioned I fitted a new oil pump two days ago.
    When the burner runs for 30 minutes or so and then locks out, resistance in the shaft is greater and it wont restart until the boiler/burner cools.
    The oil pump is relatively hot to touch when its running. It not unbearably hot that you couldn't put your hand on it.
    Any suggestions on what might be the problem would be helpful. thanks
     
  2. Sponsored Links
  3. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    why did you replace the pump.
    Did you fit a new dog ?
    Remove cover of old pump and post picture of filter and metal work.
     
  4. postflop

    postflop

    Joined:
    22 Dec 2009
    Messages:
    37
    Thanks Received:
    0
    Location:
    Belfast
    Country:
    United Kingdom
    Hi Terry
    Yes fitted a new dog. The shaft of the old pump was stiff and there was a coarse feeling when rotating it. Pump was the original on the burner, 20 years old
    Old pump is in the bin which was emptied this morning!
     
  5. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    Run a litre of oil into a clear bottle and check for water in fuel.
     
  6. postflop

    postflop

    Joined:
    22 Dec 2009
    Messages:
    37
    Thanks Received:
    0
    Location:
    Belfast
    Country:
    United Kingdom
    Just carried out that check and there is no evidence of water in the oil
    Took the cover off the fan and started the boiler, gave the fan a helping hand to rotate and away it went. I wonder is the motor not producing sufficient power?
     
  7. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,769
    Thanks Received:
    1,095
    Country:
    United Kingdom
    It is probably the capacitor needs replacing if it works with a helping hand.
     
  8. postflop

    postflop

    Joined:
    22 Dec 2009
    Messages:
    37
    Thanks Received:
    0
    Location:
    Belfast
    Country:
    United Kingdom
    Replaced the capacitor and the burner is now working. Couldn't see the wood for the trees! Had recently replaced the capacitor but the new one must have been damaged with all the other messing about! Many thanks for all your advice Terry
    The noise is still there, I described it as a warbling noise but its more like a mild grinding noise. I wonder what that could be
     