Ring main leg split

Discussion in 'Electrics UK' started by Ohmslaw, 8 Apr 2019.

  1. Ohmslaw

    Ohmslaw

    Joined:
    11 May 2013
    Messages:
    66
    Thanks Received:
    0
    Country:
    United Kingdom
    Wasnt sure how to title this.

    Just been checking the ring mains today as have recently moved in, majority fine apart from some dodgy radials from ring main.

    The fridge freezer is powered from the ring, but only one cable at socket. Upon investigation (Belling out), it seems one of the ring main legs from board, has been split and one end carries on the rest of ring main, other goes to socket for fridge freezer.

    Cant find this split, so wondering if this method is okay, and its like just spurring off one socket at the socket?

    Thanks
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,799
    Thanks Received:
    4,255
    Location:
    Retired to:
    Country:
    Portugal
    Ok.

    Spur?

    Two radials?
    What are the rating of the fuse/MCB and size of the wires?

    It could be fine depending on the answers to the above question.
     
  4. Ohmslaw

    Ohmslaw

    Joined:
    11 May 2013
    Messages:
    66
    Thanks Received:
    0
    Country:
    United Kingdom
    Looks like it's been cut into ring and spurred from there rather than at socket.

    B32 2.5mm
     
  5. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,799
    Thanks Received:
    4,255
    Location:
    Retired to:
    Country:
    Portugal
    ...but then you would have three wires in the MCB.

    That's ok for a radial/spur with only one socket (single or double); not for one with more sockets.
     
  6. Ohmslaw

    Ohmslaw

    Joined:
    11 May 2013
    Messages:
    66
    Thanks Received:
    0
    Country:
    United Kingdom
    Just 2 at board. That's why I think they've put JB somewhere, only I cant find it
     
  7. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,935
    Thanks Received:
    596
    Location:
    Herefordshire
    Country:
    United Kingdom
    have you checked the ring has continuity by removing the 2 L's from the MCB ?
    and the N
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom