Socket outlet Or Fused Spur

Discussion in 'Electrics UK' started by The Baker, 6 Jan 2021.

  1. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,962
    Thanks Received:
    1,130
    Location:
    Dorset
    Country:
    United Kingdom
    Quantum storage heaters - they INSIST the off peak supply must be in 2.5mm2 flex - even though 1.5mm2 would be ok for most sizes.

    And they INSIST the 24hr part must be a switched FCU and NOT a plug and socket.

    And if there is a fault with the heater, and the two requirements above have not been met, they will NOT honour the guarantee or help in any way.
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,807
    Thanks Received:
    4,257
    Location:
    Retired to:
    Country:
    Portugal
    As Winston keeps saying...
     
  4. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,807
    Thanks Received:
    4,257
    Location:
    Retired to:
    Country:
    Portugal
    What if you used 4mm²?

    Obviously nonsense.
     
  5. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    9,651
    Thanks Received:
    1,303
    Country:
    United Kingdom
    No, I was suggesting that a 6amp MCB offers much better protection than a 3 amp fuse.
     
    • Thanks Thanks x 2
  6. endecotp

    endecotp

    Joined:
    2 Dec 2013
    Messages:
    3,950
    Thanks Received:
    507
    Country:
    United Kingdom
    So you're suggesting that the current flows from the electrode, through the ionised gas, through the burner metalwork to the gas supply pipe, back to the gas meter, down the earth wire from the gas meter to the main earthing terminal at the consumer unit, then down the boiler circuit's CPC back to the boiler.

    This doesn't seem likely to me. I think it's more likely that the burner metalwork is connected within the boiler to its electrical earth. In fact I'd say that would be a requirement, as no boiler is likely to be double-insulated.

    Have you tried operating one of these boilers with the supply earth connection disconnected?

    Of course there is value in checking for earth continuity to the socket or FCU, e.g. as part of an EICR.
     
    • Like Like x 1
  7. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    9,651
    Thanks Received:
    1,303
    Country:
    United Kingdom
    The current involved in the sensing is miniscule, besides which the boiler control PCB senses between the pin a ground internally, so the earth loop impedance has absolutely no bearing on the flame detection system.

    I therefore suggest, that your testing of the earth loop impedance at the boiler is entirely pointless, other than to provide your electrical mates with work.

    Just to be clear, the fridge, space heater, oven and water heater in my tourer caravan - all are able to operate on bottled gas. All need a 12v battery supply to work, none need an actual connection to earth at all - everything will work quite happily sat on rubber tyres, with no 240v anywhere near.
     
    • Like Like x 1
  8. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,807
    Thanks Received:
    4,257
    Location:
    Retired to:
    Country:
    Portugal
    Not sure I really understand the concept described but - wouldn't an RCD trip with such an arrangement?
     
  9. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    9,651
    Thanks Received:
    1,303
    Country:
    United Kingdom
    It is a really tiny current, far too small to trip an RCD, besides, it is neither L to E, nor N to E. The boiler PCB's control supplies are entirely isolated from the mains supply.
     
    • Thanks Thanks x 1
  10. Sponsored Links
  11. endecotp

    endecotp

    Joined:
    2 Dec 2013
    Messages:
    3,950
    Thanks Received:
    507
    Country:
    United Kingdom
    If the current did flow through the pipework etc. then it would contribute towards tripping, but I guess it would be much too small to actually trip. Like how a small current flows to earth through interference suppression capacitors in many power supplies.

    But if the circuit is completed by a low-resistance earth connection inside the boiler (as I’m sure it must be), then no.
     
    • Thanks Thanks x 1
  12. amstel

    amstel

    Joined:
    19 Dec 2010
    Messages:
    120
    Thanks Received:
    1
    Location:
    Cheshire
    Country:
    United Kingdom
    Could I just ask a question please regarding RF lighting's answer in post 3,..."personally I prefer to install an FCU as it allows the circuit to not have RCD protection".
    I dont see why a fused plug top and socket needs RCD protection and a FCU doesn't? hopefully somebody will explain.
    Thanks.
     
    • Like Like x 1
  13. BS3036

    BS3036

    Joined:
    24 Sep 2007
    Messages:
    995
    Thanks Received:
    75
    Country:
    United Kingdom
    Sockets always need RCD protection because that is what the regulations say. The reasoning is that you could plug anything in that has e.g. a frayed cable or some internal fault which might injure someone if they touch it. A fixed installation using an FCU is 'less likely' to have such an issue. Even an FCU will need an RCD if the wiring is done in certain ways, but may theoretically be avoided.
     
    • Thanks Thanks x 3
  14. amstel

    amstel

    Joined:
    19 Dec 2010
    Messages:
    120
    Thanks Received:
    1
    Location:
    Cheshire
    Country:
    United Kingdom
    I have a washing machine and dishwasher both on their own dedicated circuits under the kitchen worktop, both on 16amp mcb's, if I changed the plug top/socket to a fixed FCU with a flex outlet, would that comply? thanks.
     
  15. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    9,651
    Thanks Received:
    1,303
    Country:
    United Kingdom
  16. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,807
    Thanks Received:
    4,257
    Location:
    Retired to:
    Country:
    Portugal
    Why would you want to do that?
     
  17. amstel

    amstel

    Joined:
    19 Dec 2010
    Messages:
    120
    Thanks Received:
    1
    Location:
    Cheshire
    Country:
    United Kingdom
    Because as it is, I think it should be rcd protected? not sure. Thanks.
     