socket tripping shower
12 Jun 2006
i was asked to look at a problem in a barber shop i am a second year apprentice electrician having just completed my exams practical and theory so i am confident working before any one asks!the barbers has three radial socket circuits and a shower circuit all protected by 63a rccb,the problem is one of the socket circuits when on will cause the rccb to trip thus turning off the electric shower!the barber is forced to leave one socket circuit dead in order to use the electric shower?can anyone shed some light on this?would be very greatful cheers
Theory ;- there is a fault on the radial that trips the RCCB
Practical ; use a meter to find the fault.
Check that the neutrals are in the correct terminals if it is a split load board.
i was also told to install an rcbo but would this be necesecary?cheers for your quick reply
Is it a split load board?
Still, I'd look at fixing the fault first :wink:. A correctly connected RCBO would just trip the socket circuit in the event of a fault.
Whatever the location or arrangement, if a power radial is tripping the rccb then there is a fault on that radial that needs to be found and fixed. You could start by shortening the radial at each of the sockets, one by one, by disconnecting the outgoing cable from either end first, to isolate where the fault is.
In a commercial or industial installation with radial circuits, RCBOs are a good start.
The loss of production caused by a general RCD trip losing other circuits will outweigh the cost of the RCBO.
This is true regardless of the (obvious) need to trace and correct the fault.
What make is the CU?