Solar panel drop outs

Discussion in 'Electrics UK' started by Chalk Philippa, 27 Mar 2019.

  1. Chalk Philippa

    Chalk Philippa

    Joined:
    27 Mar 2019
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi we recently had solar panels installed and using the monitoring app have noticed regular drop out lasting approx 5 mins each time. The company say it is normal and blame cloud cover. I do not agree as sometimes it has happened when there are no clouds and I do not believe energy production would drop to zero even if there were clouds. Also they always last approx 5 mins. Almost as though something is tripping and restarting.
    I have included an example below




    Please advise me on whether this is normal or indicates a fault.
    Thank you
    Philippa Chalk
     
  2. Sponsored Links
  3. reds42

    reds42

    Joined:
    3 Jul 2013
    Messages:
    158
    Thanks Received:
    26
    Location:
    Cumbria
    Country:
    United Kingdom
    I can't see anything attached.

    One possibility is that the main grid voltage is getting too high whilst the pannels are producing power.

    If the mains voltage gets too high the solar pannel inverter will cut out for safety reasons.
     
  4. Chalk Philippa

    Chalk Philippa

    Joined:
    27 Mar 2019
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi
    Thanks for your reply. I have tried to add the pictures again so hope it works this time.
     
  5. reds42

    reds42

    Joined:
    3 Jul 2013
    Messages:
    158
    Thanks Received:
    26
    Location:
    Cumbria
    Country:
    United Kingdom
    The sudden drops to zero output does not look like cloud problems.
     
    • Thanks Thanks x 1
  6. SimonH2

    SimonH2

    Joined:
    4 Nov 2010
    Messages:
    5,866
    Thanks Received:
    597
    Location:
    Cumbria
    Country:
    United Kingdom
    The inverter is tripping out.
    Under periods of bright sunshine, power flows in the distribution network change or even reverse - such that voltages at your supply point rise. Unless the DNO has adjusted their network to compensate, then the voltage may exceed the upper limit laid down in the standards.
    All embedded generation systems are required to have "anti islanding" protection. Basically this means that they must not try and feed an isolated section of network - whether that's just your own house, or the street, or even the whole village - should the bit of the network it's connected to become disconnected from the national grid. In theory, without such protection, it would be possible for a such a section of network to remain powered by the embedded generation with significant risks of equipment damage (eg re-closing a tripped breaker when the voltages aren't synchronised) or injury (eg to DNO personnel working on what should be a dead circuit).

    So each device must detect such a situation - and the terminal voltage going outside of limits would be one factor in this. So bright sunshine, voltage rises, inverter trips out until it decides the situation is resolved.
    My brother had exactly this problem, and the suppliers adjusted the limits to stop the trips. Go back to the installers, tell them they are spouting male bovine excrement and to adjust the limits. It may mean contacting the DNO and getting them to adjust their network. Either way, your installer should understand this and be able to sort it. I do however suspect that many installers have no idea how any of it works - and so will fob you off with any old story.
     
    • Thanks Thanks x 1
  7. ajstoneservices

    ajstoneservices

    Joined:
    1 Aug 2008
    Messages:
    6,389
    Thanks Received:
    1,099
    Location:
    Norfolk
    Country:
    United Kingdom
    Shame you cant see the voltage when it drops out. 253v perhaps?
     
  8. Chalk Philippa

    Chalk Philippa

    Joined:
    27 Mar 2019
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    That’s what I thought but the installers are insisting it is. I contacted northern power grid about voltage spikes and they advised getting installers out to check our equipment and said they could also check the voltage. If it is outside normal range they will investigate.
    I will have to be more assertive with the solar panel installers I guess.
    Clouds wouldn’t make the output zero would they unless they were very thick and black and they wouldn’t pass over in 5 minutes!
     
  9. Chalk Philippa

    Chalk Philippa

    Joined:
    27 Mar 2019
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Either they know it’s not clouds and are lying to me or they don’t know what the real issue is. Not sure which option is worst
     
  10. Sponsored Links
  11. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,124
    Thanks Received:
    3,241
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    As has been suggested, I strongly suspect it's a bit of both - they don't know what the real issue is, and so are 'pulling out of the air' (and maybe even believe) the best think they can think of ('the cloud'explanation').

    I wouldn't mind betting that, when they were wearing their marketing hats, the same company would 'reassure' you that the energy production would not fall to zero even if (during daylight hours!) there were 100% cloud cover.

    Kind Regards, John
     
    • Like Like x 1
  12. Chalk Philippa

    Chalk Philippa

    Joined:
    27 Mar 2019
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Had another drop to zero this morning and it’s just blue sky so I will give them a ring this afternoon. So I have to insist they come and have a look? I fully expect them to fob me off and tell me to contact northern power but I will stick to my guns.
    Thanks for your help.
     
    Last edited: 29 Mar 2019
  13. conny

    conny

    Joined:
    30 Jun 2008
    Messages:
    14,269
    Thanks Received:
    831
    Location:
    Suffolk
    Country:
    United Kingdom
    Tell them you have contacted Northern Power and they say/suspect the fault is with the installation. If you don't stand firm this will just keep getting backwards and forwards until you give up and just accept the situation.
     
  14. ajstoneservices

    ajstoneservices

    Joined:
    1 Aug 2008
    Messages:
    6,389
    Thanks Received:
    1,099
    Location:
    Norfolk
    Country:
    United Kingdom
    What make of inverter do you have?
     
  15. Chalk Philippa

    Chalk Philippa

    Joined:
    27 Mar 2019
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    It is a solax air x1
    Something new happened today in the monitoring app.i got an alert telling me there had been a grid voltage error. That hasn’t happened before. I have never seen an alert telling me there has been an error.
    I’m going to ask my husband to go in loft and see if the inverter display is showing any error codes.
     
  16. ajstoneservices

    ajstoneservices

    Joined:
    1 Aug 2008
    Messages:
    6,389
    Thanks Received:
    1,099
    Location:
    Norfolk
    Country:
    United Kingdom
    That readout is showing that the grid voltage (253.2v )is too high in your area that's way your inverter is shutting down, as it is meant to.

    Your installers should get the grid involved.
     
  17. arkie

    arkie

    Joined:
    4 Feb 2010
    Messages:
    73
    Thanks Received:
    5
    Country:
    United Kingdom
    Any other houses in the area with solar, or solar farms?
     
Loading...