I wonder it anyone has any thoughts on this, I am having problems with the RCD tripping.
It’s a 30mA main RCD on TT installation (overhead cables) (yes I know it should be 100mA but it normally doesn’t trip). It only trips in the morning after 7:00AM and stops at 8:00AM when my E7 switches off (but no faults on the radiators, besides they are on all night)( I think it trips as the loads switch on or off but only after 7)
Doing some more checks I found that the E to N voltage was over 8 volts during the time the tripping happens and also up to about 9:00AM then the E to N voltage drops back down to a more normal 0.8 to 1.2 V but it does vary.
The other thing is it only trips when the weather is cold, as it originally started last March, if you remember the very cold spell we had, then it didn’t trip any more until the first cold weather this winter but as it’s been mostly mild no tripping. As it’s cold again it’s started tripping again, hence more investigating.
I think I have now checked all my equipment for faults but as I don’t use anything different during very cold weather can’t think it’s that.
So is it possible for faulty equipment at another premises on my phase (or other 2 phases) to affect my trip and also cause the higher E to N voltage?
Is there something I have over looked?
Or is this situation normal for a TT install and nothing to worry about, just it’s being picked up by a sensitive RCD, if so should I just change the main RCD to 100mA and forget about it?
By the way, earthing is via 2 stakes and also bonded to the water main.
Many thanks for your thoughts, sorry it was so long.
It’s a 30mA main RCD on TT installation (overhead cables) (yes I know it should be 100mA but it normally doesn’t trip). It only trips in the morning after 7:00AM and stops at 8:00AM when my E7 switches off (but no faults on the radiators, besides they are on all night)( I think it trips as the loads switch on or off but only after 7)
Doing some more checks I found that the E to N voltage was over 8 volts during the time the tripping happens and also up to about 9:00AM then the E to N voltage drops back down to a more normal 0.8 to 1.2 V but it does vary.
The other thing is it only trips when the weather is cold, as it originally started last March, if you remember the very cold spell we had, then it didn’t trip any more until the first cold weather this winter but as it’s been mostly mild no tripping. As it’s cold again it’s started tripping again, hence more investigating.
I think I have now checked all my equipment for faults but as I don’t use anything different during very cold weather can’t think it’s that.
So is it possible for faulty equipment at another premises on my phase (or other 2 phases) to affect my trip and also cause the higher E to N voltage?
Is there something I have over looked?
Or is this situation normal for a TT install and nothing to worry about, just it’s being picked up by a sensitive RCD, if so should I just change the main RCD to 100mA and forget about it?
By the way, earthing is via 2 stakes and also bonded to the water main.
Many thanks for your thoughts, sorry it was so long.