    I am getting a summer house built in the garden. I want electrics installed and just wanted to check this is OK.

    I will have a 32amp MCB in consumer unit in my house with 10m 6mm 3 core SWA into the summer house.

    In the summerhouse I have another small consumer unit with a 20amp MCB for the sockets and a 6 amp for the lighting.

    Does this seem ok?

    Thanks in advance
     
  2. Sponsored Links
  3. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,379
    Thanks Received:
    2,106
    Location:
    Oxfordshire
    Country:
    United Kingdom
    It’s new circuits, it’s notifiable work. Ask the registered electrician that you will need. They will need to design, install, test, certify snd notify the whole thing.
     
  4. soloheadbeg

    soloheadbeg

    Joined:
    14 Feb 2011
    Messages:
    63
    Thanks Received:
    1
    Country:
    United Kingdom
    Your registered electrician might also suggest that the 32 A mcb be on the non-rcd side of your house cu and that the armour is glanded into a metal adaptable box at the house end and earthed back to the earth bar in the cu. At the summerhouse end the armour should be glanded into a plastic box or a plastic cu. The summerhouse cu would have rcd protection. This would be for TNCS system. It also assumes you won’t have extraneous metal parts (copper pipes etc.) in the summerhouse. There’s loads of interesting threads on here about this and many different views. There is no disputing it is notifiable work.
     
  5. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,094
    Thanks Received:
    381
    Location:
    Kent
    Country:
    United Kingdom
    Why do you specify a metal box at the hose end, are you one of those who wants to make a job more difficult?
    Wouldn't the summer house require a metal CU?
     
  6. soloheadbeg

    soloheadbeg

    Joined:
    14 Feb 2011
    Messages:
    63
    Thanks Received:
    1
    Country:
    United Kingdom
    Hello Suray

    I’m referring to a my own situation where the house had a plastic rather than a metal house cu. I presume you’re saying that the armour would ideally be earthed via the metal cu if present?
     
  7. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,094
    Thanks Received:
    381
    Location:
    Kent
    Country:
    United Kingdom
    The only times I have ever installed an additional box between SWA and its destination have been for access reasons or to convert to another cable [joint box], I've seen so many of these ugly add-on boxes and the majority of times I have to ask "Why?"
     
  8. Sponsored Links
  9. soloheadbeg

    soloheadbeg

    Joined:
    14 Feb 2011
    Messages:
    63
    Thanks Received:
    1
    Country:
    United Kingdom
    Fair point. My metal box is in the loft and to be honest I haven’t seen it in the nine years since I installed it so I am not reminded of its ugliness. How do you earth the armour as a matter of interest?
     
  10. soloheadbeg

    soloheadbeg

    Joined:
    14 Feb 2011
    Messages:
    63
    Thanks Received:
    1
    Country:
    United Kingdom
    Is it as I suggested by glanding into the metal cu.
     
  11. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,094
    Thanks Received:
    381
    Location:
    Kent
    Country:
    United Kingdom
    There are several standard products; Banjo rings & piranha nuts are the first 2 to spring to mind but there is nothing [apart from the difficulty of fighting it] preventing one terminating the steel wire directly into an earth bar/terminal.

    Even if glanding it into a metal enclosure, an earth wire should still be fitted.
     
  12. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,379
    Thanks Received:
    2,106
    Location:
    Oxfordshire
    Country:
    United Kingdom
    For the metal CU, that's part of it, but never trust something bolted on to a painted surface as a certain earth. I'll always use a banjo or a piranha plus an earth lead as well.
     
  13. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,094
    Thanks Received:
    381
    Location:
    Kent
    Country:
    United Kingdom
    One I pulled out last year:
    [​IMG]
     
    • Like Like x 1
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page